Wrenches,

I feel compelled to reply here, as I have personally performed all of these 
tests and listed several dozen inverters over the last 10 years.

The "Utility-Interactive" marking on listed inverters means that they meet all 
of the Utility Protective Function requirements as outlined in IEEE1547.0, and 
have been tested in accordance with the procedures detailed in IEEE1547.1.  
Most of the functions have a threshold value and a response time associated 
with them.

The Utility Protective Functions include:

Temperature stability
Abnormal voltage
Abnormal frequency
Synchronization
Interconnection Integrity
DC injection
Unintentional Islanding
Reverse Power
Open Phase
Reconnect after abnormal condition disconnect
Harmonics
Flicker

All of these tests must be performed using equipment that meets certain 
accuracy requirements, and includes considerations for "manufacturer's stated 
accuracy" of these functions.

In addition, there are utility related performance criteria in UL1741.  For 
instance, during abnormal condition tests, the maximum fault current and 
duration must be quantified and published as a rating.

Just to clarify some of what Peter wrote, the default frequency range is 59.3Hz 
to 60.5Hz, and the default voltage range is 88% to 110% of nominal.  The 
voltage must be measured from line to neutral if a neutral is present in the 
connection (i.e. a Y transformer connection).  In addition, there are outer 
boundaries that require faster trip times.

Bottom line is, if the inverter has a listing mark on it (UL, CSA, ETL, TUV, 
etc) and is marked "Utility-Interactive" there should be little or no question 
as to its' suitability for interconnection.

Hope this helps.


See ya!

Marv
Director of Technology and Support, North America
SolarEdge Technologies, Inc.
Tech Support Mobile:  +530.798.6770
Mobile: +530.392.0356


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of R Ray Walters
Sent: Tuesday, July 19, 2011 10:44 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Anti-Islanding Explanantion

If you wouldn't mind Peter, I'd like to see this discussion stay on the list.
I'd be interested to learn more about the actual anti-islanding features of 
inverters.
What you've described seems to just cover the voltage and frequency windows 
that the inverter will grid tie to.
I was always under the impression (perhaps false) that there were additional 
software controls to prevent anti-islanding to another inverter.
Bill Brooks seems to know more about UL1741 test procedures.

R. Walters
[email protected]
Solar Engineer




On Jul 19, 2011, at 10:04 AM, Peter Parrish wrote:

> I need to give a group of California educators the simplified
> explanation of inverter anti-islanding. I know the full details are
> quite complicated and have evolved a bit over the past few years, but
> would the following be an acceptable short explanation?
>
> *** Please contact me off-list with comments & edits. Thanks. ***
>
> This is an excerpt from a longer discussion about designing and
> installing grid-tied "Inverter anti-islanding is a requirement of the
> NEC and the Underwriter's Laboratory test procedures. A somewhat
> over-simplified version of "anti-islanding" says that if the grid
> voltage goes out of the range of 216 to 264 Vac or if the grid
> frequency goes out of the range 59.9 to 60.1 Hz, the inverter must
> shut down within one cycle (1/60th of a second). Once in this shutdown
> mode, the grid must come back into compliance (both frequency and
> voltage) for 5 continuous minutes before the inverter may turn on again.
> This is pretty "ho-hum". However, two of our laboratory sessions
> involve building a real, grid-connected PV system. So when our
> students go to turn on their system for the first time, they get to
> experience the "anti-islanding" function first hand."
>
> Peter T. Parrish, Ph.D., President
> California Solar Engineering, Inc.
> 820 Cynthia Ave., Los Angeles, CA 90065 CA Lic. 854779, NABCEP Cert.
> 031806-26 [email protected] Ph 323-258-8883, Mobile
> 323-839-6108, Fax 323-258-8885
>
>
>
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: [email protected]
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




************************************************************************************
This footnote confirms that this email message has been scanned by PineApp 
Mail-SeCure for the presence of malicious code, vandals & computer viruses.
************************************************************************************




CONFIDENTIALITY NOTICE: This e-mail and its attachments are intended only for 
the use of the individual or entity who is the intended recipient and may 
contain information that is privileged, confidential and exempt from disclosure 
or any type of use under applicable law. If the reader of this e-mail is not 
the intended recipient, or the employee, agent, or representative responsible 
for delivering the e-mail to the intended recipient, you are hereby notified 
that any dissemination, distribution, copying, or other use of this e-mail is 
strictly prohibited. If you have received this e-mail in error, please reply 
immediately to the sender.
P Please think of the environment before printing this email
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to