It's possible, depending on the transformer construction.

We've evaluated transformers that are spec'd up to 99% efficient,
but these were special transformers.

I don't know what type of transformer Lars was considering.


Dan


--- On Mon, 7/25/11, Dana <[email protected]> wrote:

From: Dana <[email protected]>
Subject: Re: [RE-wrenches] Efficient step up, down transformers
To: "'RE-wrenches'" <[email protected]>
Date: Monday, July 25, 2011, 10:16 AM

Seriously I have never heard of 99% eff. under load with a transformer.  Anyone 
else heard of this kind of eff. factor?  Dana OrzelGreat Solar Works, IncE - 
[email protected] - 970.626.5253F - 970.626.4140C - 970.209.4076web - 
www.solarwork.com  "Responsible Technologies for Responsible People since 
1988"Do not ever believe anything, but seriously trust through action.  From: 
[email protected] 
[mailto:[email protected]] On Behalf Of Mark Frye
Sent: Monday, July 25, 2011 9:11 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] Efficient step up, down transformers  Lars, Scary 
stuff. I worked with a system similar to this and went with big wire. The 
problem with xfrms is that you can either have low standby losses and good 
efficency at load or vis-a-versa, but you can't really have both.  Were the 
xfrms specifically wound for 120x480 conversion? If not, it is possible that 
the coil taps are connected in a manner that is not efficient. That being said, 
15.6 A @ 120V sound like an awefully large number. Perhaps you have a bad 
connection at one of your pull boxes. I would be happy to stop by and take a 
look at the xfrm spec etc. with you.
Mark Frye 
Berkeley Solar Electric Systems 
303 Redbud Way 
Nevada City,  CA 95959 
(530) 401-8024 
www.berkeleysolar.com     From: [email protected] 
[mailto:[email protected]] On Behalf Of lars Ortegren
Sent: Monday, July 25, 2011 7:43 AM
To: [email protected]
Subject: [RE-wrenches] Efficient step up, down 
transformersWrenches,                I recently installed three “ultra 
-efficient” step up-down transformers on an off grid micro grid project with a 
1500’ wire run. The grid is powered by a an old SW4024(120v) output, stepped up 
to 480v, and stepped down to 240v at two locations. I was told by the 
manufacturer that they were “99% efficient under a full load”, but upon firing 
up the system, I found a NO LOAD AMPEREAGE OF 15.6 amps!!! Needless to say, a 
completely unworkable situation for an off grid scenario, as the 840ah battery 
would be drained in a couple of hours before anything was turned on. I’m 
wondering if anyone out there has either found off grid friendly step up-down 
transformers, or if I’m just screwed and need to pull parallel 4/0 runs 
(probably the price of a new car) to fix the problem. HELP!  Lars Ortegren  
Director of OperationsCalifornia Solar Electric
 Company10141 Evening Star Drive, Suite 6Grass Valley, CA 95945  Phone : 
(530)274-3671Fax: (530)274-7518  
-----Inline Attachment Follows-----

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to