It sounds like you want an AC system for your "home theater" system, so make sure you get a mobile rated inverter if you plan to have a backup AC source. That way you will have integral neutral-ground bond switching. The mobile versions are rarely much more $, if at all. Try Magnum or Outback.
And make sure you plan for a satellite dish so you can pick up curling matches. Jason Szumlanski On Aug 9, 2011, at 9:09 AM, "Exeltech" <[email protected]> wrote: > First .. why are you grounding a portable system? It's not required. > > In [29 CFR 1926.404(f)(3)(i)], OSHA states the frame of a portable > generator need not be grounded (connected to earth). > > If it's a fuel-powered generator, the NEC 250.34 states the frame may > serve as the ground as long as normally non-current-carrying metal parts > of equipment and the equipment grounding conductor terminals of the > receptacles are connected to the generator frame. > > This is even more applicable if the system is all low-voltage DC only. > > > Dan > > > _______________________________________________ > List sponsored by Home Power magazine > > List Address: [email protected] > > Options & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out participant bios: > www.members.re-wrenches.org > _______________________________________________ List sponsored by Home Power magazine List Address: [email protected] Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org