Wrenches: Followup on my earlier post about the XP125: Dan at Exeltech has stepped up in a major way. Here are a few quoted excerpts from a set of emails he has sent me about this: 1. Cause and solution: Certain of the new electronic chargers (such as De Walt, Craftsman (usually made by De Walt, etc. and branded "Craftsman"), and others are highly capacitive on their input. In certain instances, this can drive our voltage control loop unstable in the smallest inverters. Anything that looks larger than approximately 1 microfarad might do this - but again .. only for our *smallest* inverters, such as the XP125 and XP250. Our larger inverters (>600W) and our new designs do not exhibit this sensitivity. If any of our inverters are going to be used with a capacitive load, let us know and we will provide free of charge a component for to you to wire in series with the inverter AC output that will counteract the effects of a capacitive load. Also .. since a capacitive load appears to be the situation with your customer, please contact me at the office on Monday and I will authorize the repair of her unit free of charge. We will also include the component (referenced above) for connection in series with the inverter when you re-install it. 2. What the fix is, and why it's done this way: In the case
of the XP125 (sorry, no pun intended), there's not
sufficient room inside the unit to add the inductor -
hence external mounting and connection (anywhere you
like). You could install it into the "line" lead of a
power strip and it will do the job perfectly. Also ..
there's an issue if we modify anything internal to the
inverter. It's UL Listed .. and if we even change the
paint color .. UL gets involved. If *we* install the
inductor .. it affects our UL Listing. If *you*
install the inductor .. UL doesn't care.
#2: The
inductor can be installed in the circuit used for any
and all loads. No need to have it carry the power for
just the charger. Install it inside the power
strip, solder the inductor in series with the "line"
conductor, then have that strip feed all of the loads
that will ever be used, just as they're doing now.
#3: Unasked
question: Why don't we do this for all of the
inverters?
First ..
because this issue didn't become a problem until quite
recently, and only then with some of the new
electronic chargers. Second .. the "fix" is
needed only for a tiny fraction of the units we
manufacture, and we're doing all we can to help keep
the cost down for you and your customers.
Our
higher-wattage inverters don't tend to be affected by
electronic chargers because the charger's capacitance
is a far smaller percentage of our large inverter's AC
output capacitance (compared to the XP125), and thus
isn't generally an issue. The only time a larger
(e.g. 1100 watt) inverter may be affected would be if
you were to plug in [say] six to ten of these
electronic chargers into that inverter all at once --
in which case the corrective action is an inductor
(the same as for, but a larger inductor than for the
XP125) .. and again one we'd provide free of charge.
3. About my Wrenches post that turned out to include incorrect information: The
source of the misinformation has been found. He was
forced to eat liver-pate and peanut-butter sandwiches on
raisin bread, while drinking warm milk and listening
repeated renditions of the Macarena Song.
All
kidding aside .. you spoke with a tech who started on
the production floor and graduated into our Service
Department. He's actually very good at what he does,
but like any of us .. not perfect. He acknowledged
telling you the information you reported on the Wrench
BBS. Turns out it was based on his opinion rather than
fact. The overload protection circuits in our larger
inverters are obvious, as they involve [of course] more
[and larger] parts. The 125, being comparatively
low-power, has a physically smaller and less
visible protection circuit (but being only 1 amp output,
the circuit doesn't need to be very big). Since the
circuit didn't jump off the PC board to his eyes (so to
speak).. he [unfortunately] presumed it wasn't there --
and that's the information he passed along to you. He's
been apprised of the correct info, and he expressed his
sincere regret and apology for the inadvertent
misinformation he shared.
I've
instructed our Customer Service Dept to fix the inverter
at no charge. I'm doing this not because of your post
on the BBS .. but instead, as you described it .. it's
the right thing to do. I will hope you'll be as vocal
on the BBS about good service .. and also to
correct/update the info to the Wrenches .. which I admit
was passed along to you in error .. but only if YOU feel
it's the right thing to do as well. As we all know of
our customers, happy ones don't tend to say much ..
while the rare unhappy ones never seem to be quiet.
To
that end .. If there's ever anything passed along to you
from anyone at Exeltech that you question or make you go
"hmmmmm" .. you are welcome and encouraged to contact me
at any time for verification/clarification. It's much
easier to fix before it happens, rather than print the
proverbial newspaper retraction, which never seems to
get the high-level attention of the original erroneous
story.
So I am being "vocal on the
BBS about good service .. and also to correct/update the
info to the Wrenches". Exeltech is taking care of the
issue in a good way. I'm happy to pass that news along to
this list.Allan Allan Sindelar [email protected] NABCEP Certified Photovoltaic Installer NABCEP Certified Technical Sales Professional New Mexico EE98J Journeyman Electrician Positive Energy, Inc. 3201 Calle Marie Santa Fe, New Mexico 87507 505 424-1112 www.positiveenergysolar.com -------- Original Message --------
EDITED:
|
_______________________________________________ List sponsored by Home Power magazine
List Address: [email protected] Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org