I've also used 250.52A(7) defining plate electrodes. A 6" Sch 40 pipe 4
ft in the ground has more than the required 2 sq ft of surface metal,
and is at least the required 1/4" thickness.
Also, the 2011 NEC dropped 690.47 D which required a grounding electrode
at the array. Are you sure you still need this? I believe 2011 only
requires you bond all the metal to the EGC, as always.
Ray Walters
On 9/30/2011 8:24 AM, Kent Osterberg wrote:
The requirements listed in 250.52(3) were changed in 2011. The rebar
used is allowed to be near the bottom of the footing or in vertical
foundation walls that are in direct contact with earth. If there was
in doubt in the past that the rebar in the concrete of a pole mount
was a suitable grounding electrode, the changes in 2011 should remove it.
Kent Osterberg
Blue Mountain Solar, Inc.
Richard L Ratico wrote:
As Dan points out, 250.52(A)(3) specifies several installation
requirements in
order for a concrete encased electode to qualify as a permitted
Grounding
Electrode. A pole mount foundation would certainly qualify if it met
those
requirements.
Even if the requirements are not met, IMHO, any opportunity to
inexpensively
increase the grounding integrity of a system should not be overlooked,
particularly in lightning country. Of course, a code compliant Grounding
Electrode System is still required. Bonding a non compliant, but
never the less,
very substantial additional "electrode" to that system would not hurt
anything
and quite possibly help considerably.
Dick Ratico
Solarwind Electric
_______________________________________________
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org