Wery well said Gary, the service drop and service lateral serve to limit the 
AFC, 
 
I did not mention that large switch gear has to have With Stand Current rating 
also which means if subject to a short and the AFC the gear shall not distruct 
from the mechanical forces generated by the magnetic fields.  In the case I 
mentioned the busbars were ripped from their mounts and the cabinets were 
pulled into the mess.  ( ever see welding cables snap together when a high 
current passes?  

From: Gary Willett <[email protected]>
To: [email protected]
Sent: Monday, October 3, 2011 3:32 PM
Subject: Re: [RE-wrenches] interrupting current calculations used to determine 
the interrupting of the AC equipment.


James:

I believe your PE is referring to the short circuit current
      calculations of 110.10, and the 110.24 marking requirements for
      AFC (Available Fault Current). The utility company should be able
      to give you the AFC at the secondary of their transformer, or
      better yet - at the service equipment.

The short circuit current rating of the utilization equipment, and
      the AIC (Available Interrupting Current) rating of the OCPD in the
      utilization equipment, must exceed the AFC.

 
 
Regards,

Gary Willett, PE
    

> 
>From:[email protected] 
>[mailto:[email protected]] On Behalf Of James Rudolph
>Sent: Monday, October 03, 2011 1:54 PM
>To: RE-wrenches
>Subject: [RE-wrenches] interrupting current calculations used to determine the 
>interrupting of the AC equipment.  
>  
>Dearest Wenches,
>
>    I received an e-mail from PE reviewing one of our projects
          to build, and this is what they wrote-
>
>No interrupting current calculations were included.  It is
            suggested the utility company be consulted for available at
            the service entrance and these values be used to determine
            the interrupting of the AC equipment.
>
>Does any one out there have experience dealing with this
          issue, or have the ability to shed some light on this subject.
>
>Many thanks in advance,
>
>-- 
>James B Rudolph
>NABCEP Certified PV Installer
>
>  
> 
>
>_______________________________________________
List sponsored by Home Power magazine List Address: 
[email protected] Options & settings: 
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & 
etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: 
www.members.re-wrenches.org    
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to