Hi Orion.

Go into locked menu

systems menu
inverter
stacking

in the stacking menu is where you set it all up

And I take it you are not using a balancing transformer, curious why not?

Can't tell you anything about the AGS, but interested to know what the problem 
is.

jay

peltz power


On Oct 30, 2011, at 10:29 AM, Orion Thornton wrote:

> Hi Wrenches,
>  
> I was hoping I may be able to get some guidance on navigating through the new 
> MATE3 controller.  We have a customer that swapped out their original MATE 
> for the MATE3 in order to have access to on-line monitoring of their system, 
> since it is a part time residence with limited access and unoccupied in the 
> winter.
>  
> Since the new controller was installed they have had issues with the AGS.  I 
> was on site last Friday and was able to sort out the AGS issues, at least I 
> thought I had.  I left the site with the generator charging the batteries.  
> After the generator had ran for about 5 hrs and the battery voltage read 51.5 
> volts the customer called concerned that the generator had not shut down 
> after the charge reached a float level.  They turned the generator off and at 
> that point lost half the loads in the house because the slave inverter had 
> shut down.   I can see that the inverter mode is “off” through the on-line 
> monitor.
>  
> I will probably be heading back up to the site tomorrow for more 
> troubleshooting, but at this point I would really like to be able to guide 
> the customer through getting the secondary inverter turned back on so they 
> have all their loads powered up without running the generator.   This is the 
> first time I have worked with the MATE3 and have searched high and low 
> through the manual to try and find how I can access the mode setting for the 
> slave inverter, so that I can turn it back on, but I have found nothing.  If 
> it was a weekday I am sure an Outback tech could send me in the right 
> direction, but I am hoping someone out there in the wrenches world has got 
> the MATE3 dialed in.
>  
> Any input would be much appreciated.
>  
> Thanks.
>  
> Orion Thornton
> Project Manager
> Independent Power Systems
> NABCEP Certified PV Installer
> (Office) 406.587.5295
> (Mobile) 406.249.9912
> www.solarips.com
>  
>  

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to