jm7 y first thought is a bad neutral connection, it could be heavy neutral
current do to harmonics, The grow lights put a load on the neutral by third
harmonic. I have seen a switch gear burn up after we put the school on
electronic balasts.
Darryl
________________________________
From: Nathan Jones <[email protected]>
To: [email protected]
Sent: Sunday, November 13, 2011 3:12 PM
Subject: Re: [RE-wrenches] Strange voltage readings, power quality
Mac,
I have encountered two battery based inverters that were affected by the
feedback frequency of CF bulbs. One would trip and show overload from a single
15 watt bulb with no other loads connected every time. The other one was an
intermittant situation. Had I not encountered this problem before I might still
be trying to figure that one out. I think it would be worth ruling out as a
possibility at this point.
Nathan Jones
Power Source Solar
417-827-0738
On Sun, Nov 13, 2011 10:55 AM CST mac Lewis wrote:
>Hello wrenches,
>
>I am having an interesting grid-tied issue and would love to get some input.
>
>The installation is 3 Fronius IG Plus inverters all single phase, two 7.5s
>and one 10.0. The service is 120/208. We have the two 7.5s feeding a
>dedicated 3 phase sub and tied back into the main panel after production
>meter. The first 7.5 is tied across Va to Vb, the second is tied in across
>Vb to Vc. The 10.0 feeds directly back to the main panel after production
>meter and is tied in across Va to Vb.
>It should be noted that this facility has very large capacitive load, about
>25 kW of grow lights. According to an egauge on site, the power factor
>ranges from 0.5 to 0.75 on all phases.
>The system worked flawlessly for 3 months, suddenly the two 7.5s dropped
>out and gave a myriad of grid errors, everything from islanding errors, to
>high grid voltage, and low grid voltage etc.
>
>I went over there and found the phase B voltage to neutral, was way out of
>wack, anywhere from 120-170. Oddly, the Line to line voltage was fine,
>right around 208 for all phases. I called the power company and had them
>install a monitor at the transformer. After 5 days they came back and said
>that their end was within spec. I decided to put both of the 7.5s between
>Va to Vc. They would not boot up. I then went to the main panel and
>changed the physical location of the breaker for the subpanels of the 7.5s.
> This seemed to make the difference. They booted up and are exporting
>power. I tried switching one of the 7.5s back Va to Vb, but it still would
>not boot up unless it is connected from Va to Vc.
>
>My working theory right now is that we are getting harmonics traveling back
>to the inverters from the ballasts on the grow light across line B. As far
>as explaining why it suddenly happening, my guess is that he has started
>turning off inductive loads such as fan motors and compressors as we are
>entering the winter. There may have been a filtering effect going on with
>the motors absorbing some of these harmonics and attenuating them. I am
>going to try to verify this with an oscilloscope this week.
>
>Does anyone have any other theories to explain this type of behavior?
> Anyone seen this before? Should I look for anything else?
>
>Thanks
>
>Mac Lewis
>
>
>--
>
>
>
>Mac Lewis
>
>*
>
>"Yo solo sé que no sé nada." -Sócrates
>*
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org