y seem to be on top of the situation.  I would use the MPPT wattage of the 
array for my source wattage.  devide by 480 volts and 1.73 for three phase and 
you have the current per leg.to do your voltage drop calcs from.   IO have not 
always been carefull to keep similar phases apart, but you will probibly buy 
your direct burrial in the form of triplex so lay them like you buy them.  Of 
course do not runn through metal holes unless balanced currents.  Also any time 
you make a short run, KEEP the length the same.  
 
DT 


________________________________
From: Luke Christy <[email protected]>
To: [email protected]
Sent: Wednesday, November 16, 2011 9:51 PM
Subject: [RE-wrenches] 3-phase wire run considerations


Hi Folks,
In several months we will be installing a 100kW ground mounted PV system for 
one of our commercial customers. I'm in the planning stage and am looking at 
the wire runs. The site requires a 700' underground wire run between the 480V 
service and the single central inverter located at the array (a PVP100kW unit). 
I have two related questions: 
1: Given the significant cost of the AC cabling for this situation, what is the 
most appropriate number to use for current in running voltage drop calcs? The 
wiring is going to be significantly oversized to achieve a ~1% VD at this 
length. I could use the max rated output current of the inverter (120A), but 
that seems like it might be overly conservative. Opinions?

2: It looks like the most cost effective and manageable solution for this run 
will involve several paralleled sets of cables. How important are the 
considerations of careful cable bundling? ie: putting several conductors per 
phase willy nilly in a trench vs having separate triplexed bundles.

Thanks in advance for your thoughts.


  

Luke Christy 

>NABCEP Certified PV Installer™: Certification #031409-25 (Luke Christy)
NABCEP Certified Solar Thermal Installer™: Certification #ST032611-03    
> CoSEIA Certified PV Installer (Luke Christy)
>
>Solar Gain Services, LLC
>Monte Vista, CO.
>[email protected]

>





_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to