Larry, the customer has been fully charging and equalizing every week to two 
weeks for several years. They also are diligent about checking the batteries 
with a hydrometer. It turns out then that I, and the customer, have put too 
much faith in hydrometer readings to give an accurate picture of battery 
health? Yes I agree (long time ago) the battery monitor would have been helpful 
in catching the problem - if this is the problem. A couple of other posters 
have suggested another possibility: a fractured bus bar inside the battery or a 
dead cell. Both of these suggestions came from people who experienced almost 
identical problems that were extremely difficult to detect. I have recovered 
several sets of sulphated batteries, Surrettes, Trojans, Yuasa, so I know what 
they are like and what they smell like when subjected to a high amp charge.

I have several sets of these KS25's & 21's in the field and for the most part 
they have worked very well but I've seen customers sulphate L-16's in a few 
weeks of deficit charging, it just takes longer with a big battery especially 
when they aren't really being abused.

I'm sure hoping the horse hasn't left the barn on this one.

Ron Young
 
On 2011-11-17, at 12:32 PM, Larry Crutcher, Starlight Solar Power Systems wrote:

> Ron, 
> 
> From what Daryl said below and the fact that your customer has about 15 amps 
> of PV charge, you should deduct that the batteries have MOSTLY been deficit 
> charged their entire life.  Here's what I told you on Oct 22 in my lengthy 
> explanation about what the problem is and why it happened: "Undersized RE 
> charging systems, or perhaps oversized batteries, is the culprit that 
> contributes to this all too frequent phenomenon of chronic undercharging." 
> 
> You said that the customer has been compensating for an undersized system by 
> running a generator. They can not know this because there is no monitor. The 
> batteries now have a sulfation problem, perhaps unrecoverable, that could 
> have been prevented if the owner had a battery capacity monitor. This is not 
> pleasant news, I know. I have to explain this bad news to people MANY times 
> each week. This is a huge issue globally. And such waste of money, time and 
> resources just bugs me!
> 
> Larry Crutcher
> Barer of Bad News
> Starlight Solar Power Systems
> 
> On Nov 17, 2011, at 5:17 AM, [email protected] wrote:
> 
>> Ron,
>>  I'm going to reiterate what Jeff says here. It is similar to what I had
>> said in my email. The charge rate must REGULARLY be C10 on the KS 
>> (5000 series) batteries. This means, on KS 25's, a routine bulk
>> charging rate of 135 amps. I find that on these types of hybrid
>> systems, while the batteries might occasionally (sunny day, generator
>> running, etc.) that kind of charging, they do not regularly see C10. I
>> think if you gave Jamie Surrette a call he would give you the same
>> possible assessment.
>>  I do think the problem is oversulfation, but none of this solves your
>> problem, I know. We have been installing KS series batteries since they
>> came out and this necessity of regular C10 charging has been an
>> integral  part of design for me for many years.
>> 
>> Best,
>> Daryl
>> 
>> 
>> 
>> 
>>> Ron,
>>> 
>>> 
>>> 
>>> This reply a little late since I have been off line a few days.  I
>>> mentioned
>>> in a similar thread last year that I had an off grid home client I
>>> designed
>>> and installed in Idaho back in 1998 that had a Kohler 8.5 kw generator, a
>>> Trace 4024 inverter, two separate solar arrays and Outback charge
>>> controllers, and 16 Trojan "L-16" batteries.  This system worked
>>> flawlessly
>>> for 7 years and only required the generator a few hours per month, then it
>>> was time to change the batteries.  I replaced the Trojans with the same
>>> size
>>> battery made by Surrette and everything went to crap.  They had to run the
>>> generator hours and hours to get them past an 80% charge and we had lots
>>> of
>>> problems with overloading the generator even though we did not make any
>>> program changes and used the same generator.  The generator was replaced 2
>>> years later but this system  never worked like it did before the battery
>>> replacement.
>>> 
>>> 
>>> 
>>> When researching all this at that time I had talked with Surrette, Trojan,
>>> and anyone else that might help and this is what I found out.  Of course
>>> there are just my opinions based on these conversations, but it is my
>>> understanding that Surrette is a much longer life battery with much less
>>> water loss when comparing apples and apples, and I was told this was due
>>> to
>>> a different lead composition that Surrette uses than any other battery
>>> manufacturer.  However, this difference requires a much longer
>>> absorption/taper off charge process or you will never get it past 80%
>>> charged.  This of course is almost impossible to achieve with a generator
>>> or
>>> undersized solar array, and you really need a grid connection to fully
>>> charge these things.  No doubt these would be great in some standby grid
>>> connected system but I no longer use them in off grid.  This was also at a
>>> time when battery manufacturers were just discovering solar so maybe
>>> battery
>>> designs have changed.  Again, I think Surrette is a good company and makes
>>> a
>>> great battery, but just not sure you can fully recharge them with a
>>> mid-sized generator.
>>> 
>>> 
>>> 
>>> I also do not like using parallel battery layouts as its hard to keep one
>>> string from pulling down the other strings when there is a low performance
>>> cell so you might do a cell by cell check.
>>> 
>>> 
>>> 
>>> Good Luck,
>>> 
>>> 
>>> 
>>> Jeff Yago
>>> 
>>> DTI Solar Inc.
> 
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: [email protected]
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to