Ray, I'd use the 2% high temp. The 0.4% high temp would only be reached a few hours out of the year. However, the 0.4% high is only a few degC warmer than the 2% high, so that would change my fudge factor below by a max of 1.8-2.0%.

On 2011/12/1 15:48, Ray Walters wrote:
That's more detailed info, but I still am wondering what ambient temp to
apply (which AHSRAE #) with the temp adder. Daryl suggested using a 2%
high temp. Also, where are you all getting your weather data? I found
the NEC suggested ASHRAE manual to be close to $200. That's a bit much
just to get a couple of numbers for our design.
It seems this calculation of low voltage is far from being entirely
codified, and I'm trying to standardize it somewhat for my PV class. Non
of the design manuals I have currently are even close to this level of
complexity, yet this is obviously an important calculation. Should I
suggest that my students just use the inverter manufacturers' online
tools, and forget about trying to run this voltage calc themselves?

Thanks,

Ray

On 12/1/2011 6:30 AM, Dave Click wrote:
At an SMA training last year they recommended the following
temperature adders:

Open field: +22°C
Rooftop, lots of ventilation: +28°C
Rooftop, some ventilation: +29°C
Rooftop, little ventilation: +32°C
Rooftop BIPV, no ventilation: +43°C
Façade, some ventilation: +35°C
Façade, little ventilation: +39°C
Façade BIPV, no ventilation: +55°C

For your Sanyo project, I'd agree that the pole mount would be a good
fit and +25C would seem to be OK. As you know, the 301VDC VMP on an
inverter with a 300V+ tracking window wouldn't work very well during
the summers for very long. My own rooftop system has a design VMP of
around 294 at 70C module temperature and I've seen it a bit lower than
that on a sunny day-- I think it's because in irradiances below
1000Wm/2, the modules can still get plenty hot but the lower
irradiance doesn't bring the VMP up to 100%. So all told, maybe plan
for an array minimum of:

Inverter Tracking Minimum
/0.85 (degradation and voltage tolerance)
/0.95 (effect I just described)
/0.825 (60C operating temp)
= minimum string VMP at STC

(similar to what Bill said)

On 2011/11/30 11:04, Kirk Herander wrote:
Thanks for all the good response. Speaking of monkey wrenches, these are
Sanyo HIT Double panels, mounted on a rack which is 5 ½ feet above the
roof surface. They will absorb reflected light on the backside, so I
assume the cells will operate at a higher temp. But they are elevated
enough to simulate a pole-mount, thus lowering operating cell temp. So
what operating temp to use? If I use 25 C as the operating temp, the low
voltage calc comes out to 301 vdc (inverter min is 300 – using SMA
US8000). If I use 15 C the calc is 308 vdc. This is for a 6 panel
string. Unfortunately I really don’t want to use 7 panel strings due to
the layout. If I used a US7000 it would work since min vdc in is 250.
However the inverters are part of a SunnyTower and I can’t swap a 7000
for an 8000 without voiding the Tower UL listing.

Kirk Herander

VT Solar, LLC

dba Vermont Solar Engineering

NABCEP^TM Certified installer Charter Member

NYSERDA-eligible Installer

VT RE Incentive Program Partner

*From:*[email protected]
[mailto:[email protected]] *On Behalf Of
*[email protected]
*Sent:* Wednesday, November 30, 2011 1:03 AM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] calculating low string voltage



If you really want to throw a monkey wrench into the mix, bring up
partial shading...

Or, maybe that's just not allowed in that debate ?? Just a thought.

boB







On 11/29/2011 8:39 PM, Kent Osterberg wrote:

Kirk,

You've got some good feedback on this from Ray and Bill. I'll try to add
a little more. Most module datasheets show a normal operating cell
temperature, NOCT, value that's typically 47.5°C. That's 20°C ambient
temperature, 800 W/sq m, and calm wind and nothing blocking the airflow
on the back of the module. That 27.5°C temperature rise should be pretty
close to the temperature rise that occurs for a pole-top mount. It's
common to see people use 25°C for modules on a pole and 30°C or 35°C on
a roof and there are data that support these "typical" values. With 1000
W/sq irradiance, the temperature rise can obviously be more too. Between
the intensity of the sun, the direction of the sun, the color of the
roof, the spacing off the roof, and the wind speed there is a lot that
is different from one system to the next or even one day to the next.

Most PV module spec sheets don't give you a temperature coefficient for
Vmp. I've seen people use the the Voc coefficient, usually expressed as
a percentage, for both Voc and Vmp. Big mistake. Data from NREL
indicates as Bill said, the temperature coefficient for Vmp is higher
than that the temperature coefficient for Voc. That's particularly true
when the coefficient is expressed as a percentage per °C. Since there
are very few manufacturer's that give both temperature coefficients,
I'll use a value from an old Evergreen module for an example. The
Evergreen ES-195 datasheet shows Voc = 30.5 volts with a coefficient of
-0.34%/°C and Vmp = 27.1 volts with a coefficient of -0.47%/°C. Since
one shouldn't add volts and percents, I'll put the temperature
coefficients in volts/°C: Voc = 30.5 V - 0.10 V/°C and Vmp = 27.1 V -
0.13V/°C. So Vmp is moving faster than Voc, but not a lot faster. That's
generically true for c-Si or poly-Si.

Kent Osterberg

Blue Mountain Solar, Inc.

www.bluemountainsolar.com <http://www.bluemountainsolar.com>

t: 541-568-4882


On 11/29/2011 11:48 AM, Kirk Herander wrote:

I am in debate with a PE over calculation of low voltage of a series
string on a hot day. He insists that an arbitrary high cell temp is
factored in, not just ambient temperature. Could someone please give an
accepted formula for this calculation? Thanks. I cannot find a clear
reference to low voltage calculation on a hot day (but every reference
material is clear on how to calculate high voltage on a cold day).

Kirk Herander

VT Solar, LLC

dba Vermont Solar Engineering

NABCEP^TM Certified installer Charter Member

NYSERDA-eligible Installer

VT RE Incentive Program Partner






_______________________________________________

List sponsored by Home Power magazine



List Address:[email protected]
<mailto:[email protected]>



Options& settings:

http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org



List-Archive:http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org




List rules& etiquette:

www.re-wrenches.org/etiquette.htm
<http://www.re-wrenches.org/etiquette.htm>



Check out participant bios:

www.members.re-wrenches.org <http://www.members.re-wrenches.org>





_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options& settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules& etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org





_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to