You might also point out Section 690/3 of the NEC: 690.3 Other Articles. Wherever the requirements of otherAllan
Allan Sindelar
[email protected] NABCEP Certified Photovoltaic Installer NABCEP Certified Technical Sales Professional New Mexico EE98J Journeyman Electrician Positive Energy, Inc. 3201 Calle Marie Santa Fe, New Mexico 87507 505 424-1112 www.positiveenergysolar.com
On 12/8/2011 9:42 AM, Hans Frederickson wrote: Jason, I agree that the inspector is wrong. I see two options: 1) Appeal the inspectors ruling with his supervisor(s). 2) Cut in a little flush mount service disconnect adjacent to the main service panel. You could use a 2-space flush-mount panel like Cutler Hammer CH2L125FP. This is rated for service entrance use, but does not include a visible break disconnect (just a breaker), so depending on your utility's requirements, it might need to be redundant to your fused disconnect outside.Regards, -Hans From: [email protected] [mailto:[email protected]] On Behalf Of Jason Szumlanski Sent: Thursday, December 08, 2011 5:22 AM To: RE-wrenches Subject: [RE-wrenches] Grouping of Service Disconnects I know this has been discussed ad nauseum, but. I have a supply side tap with a fusible disconnect located next to the meter outside. The tap is in the main distribution panel which is back to back with the meter inside a finished garage. There is a 200A main breaker in the MDP. The inspector is insisting that the solar AC disconnect (fusible disconnect) be located inside the garage next to the MDP. He is saying that service disconnecting means must be grouped. The inspector acknowledges that the PV system is considered a separate source, not necessarily a separate service, but also insists that Section 230 applies. I pointed out that section 230.72(A) and 230.71(A) apply to grouping of service disconnects for the SAME service, not grouping of all disconnects for multiple services. I noted that the location required in 230.70(A)(1) allows for the disconnect to be outside the building. There is no explicit requirement for disconnects of separate services to be co-located (grouped). I also pointed out 690.56(B) which implies that the PV system disconnect can be located elsewhere if a plaque or directory is supplied. I thought this was case closed, but he is still not seeing it my way. I realize that the AHJ could theoretically make the determination that the disconnect be located inside, but that is not the case he is making. He is stuck on the grouping aspect. I have provided Enphase's white paper on disconnecting means and the excellent IAEI articles on the subject. I think they are interpreting the word "each" in 230.71(A) to mean "all." I'm not sure. There is no way that the homeowner will allow a surface mounted fusible disconnect next to his flush mounted MDP in the garage. The next best alternative to comply with the inspector is expensive and time consuming, and a load side connection is out of the question. Not happy right now. Jason Szumlanski Fafco Solar _______________________________________________ List sponsored by Home Power magazine List Address: [email protected] Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org |
_______________________________________________ List sponsored by Home Power magazine List Address: [email protected] Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org