Dan,

While the battery box, or maybe the whole room they are in, do fit the definition of a Class 1 Division 2 location, I don't think it is consistent with the intent of that section. Wring methods for hazardous locations are specifically designed to keep the wiring isolated from the hazard. That notion doesn't work batteries - they are the source of the hazard and the wires do run to, and into, them. To be complaint with the requirements for hazardous locations the batteries would have to have integrated gas tight junction boxes enclosing the terminals. And interior of the battery would still remain an explosive environment with energized conductors no matter what is done to wiring on the exterior of the battery. Batteries are a special hazard and wiring methods specified for Class 1 Division 2 locations won't mitigate that hazard.

It takes a lot of ventilation to keep the H2 levels below the explosive threshold.

Kent Osterberg
Blue Mountain Solar, Inc.
www.bluemountainsolar.com
t: 541-568-4882


On 12/14/2011 4:46 PM, [email protected] wrote:
I've mentioned it in the past, and got the impression it went over like a fart in church, but it seems to me buttoning up a battery box tighter than a bull's ass in fly season, and (hoping) mechanical ventilation mitigates this creation of a hazardous environment creates a Class I, Division 2 location. (NEC 500.5 (B)(2)(2)).
Any takers?
db


Dan Brown
Foxfire Energy Corp.
Renewable Energy Systems
(802)-483-2564
www.Foxfire-Energy.com <http://www.Foxfire-Energy.com>
NABCEP #092907-44


    -------- Original Message --------
    Subject: Re: [RE-wrenches] NEC 480 - battery enclosure question
    From: Ray Walters <[email protected] <mailto:[email protected]>>
    Date: Wed, December 14, 2011 11:52 am
    To: RE-wrenches <[email protected]
    <mailto:[email protected]>>

    110.11 Deteriorating Agents. Unless identified for use in
    the operating environment,no conductors or equipment
    shall be located in damp or wet locations; where exposed to
    gases, fumes,vapors, liquids, or other agents that have a
    deteriorating effect on the conductors or equipment; or
    where exposed to excessive temperatures.
    Informational Note No. 1: See 300.6 for protection against
    corrosion.

    110.18 Arcing Parts. Parts of electrical equipment that in
    ordinary operation produce arcs, sparks, flames, or molten
    metal shall be enclosed or separated and isolated from all
    combustible material.

    300.6 Has a lot of good info on corrosion that we in the solar biz
    should be all over, as well.

    So that's 3 pretty specific code references.

    Ray Walters

    On 12/13/2011 7:03 PM, [email protected] wrote:
    On 12/13/2011 5:47 PM, Dan Fink wrote:
    Esteemed Wrenches;
    An email question from my recent Home Power article on charge
    controllers that I'm unsure of.
    Does NEC specifically forbid mounting other gear, such as charge
    controllers, inside a battery enclosure? How about shunts?
    It's not in 480 that I can see, and 480 doesn't seem to treat
    the interior of a battery enclosure as particularly explosive,
    because as per 480 it has to be adequately vented anyway.
    Of course there are a zillion common-sense reasons not to
    actually DO that -- even an MX60 has a relay that can spark--
    and of course corrosion on the controller terminals, circuit
    board, etc. Bad news all around and I never do it.  I learned
    this as an apprentice back in the 1990s, and I just don't do it.
    But I do put shunts in there sometimes...is this a no-no? The
    shunt terminals are brass, I've never seen any really nasty
    corrosion build up, but I'm quite curious.
    BUT I'm wondering  if I'm missing something obvious in some
    other NEC section etc.

    Thanks in advance!



    Hi Dan.   Nice article, BTW !


    The NEC doesn't say that you CAN do this, but it does not
    dis-allow it either.

    It will come down to what the battery manufacturer says, is what
    we have found.

    Sealed batteries are the only ones that can be mounted in a
    battery box with
    arc and spark equipment.

    Look at UPS's that you buy from COSTCO for instance.  They are UL
    listed, usually.

    boB


    _______________________________________________
    List sponsored by Home Power magazine

    List Address: [email protected]

    Options & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm

    Check out participant bios:
    www.members.re-wrenches.org




    ------------------------------------------------------------------------
    _______________________________________________
    List sponsored by Home Power magazine

    List Address: [email protected]
    <mailto:[email protected]>

    Options & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>



_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options&  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules&  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to