Hullo Hugh;

Perhaps I could state it better, that each string of series LEDs needs to have its own current limiting device (a resistor or regulator).

The reason I advise that is that all LEDs vary a bit in their volt/amp/lumen performance curves, especially between batches, but even within a batch. If you were to put 2 "identical" LEDs in parallel sharing one current limiting resistor, one LED is *always* going to draw more current than the other and be brighter. If the difference is too great, the one drawing more current will burn out first. If you are lucky with your matching, it might not be problem for a very long time, but I've also seen burnout happen between batches in just a few minutes.

It's a positive feedback loop (thermal runaway). As an LED heats up, forward voltage drops and current increases.

So, by current limiting each string you avoid both the variable brightness problem and the thermal runaway problem.

This is a pretty good article on the topic:
http://www.ledsmagazine.com/features/4/8/1 <http://www.ledsmagazine.com/features/4/8/1>

It's nice that we can all purchase decent LED lighting products these days and not muck about with breadboards and soldering irons like we had to a few years ago. A good inexpensive compromise is to regulate all the strings with a single DC power supply, then current limit each string with a resistor.

--
Dan Fink,
Executive Director;
Otherpower
Buckville Energy Consulting
Buckville Publications LLC
NABCEP / IREC accredited Continuing Education Providers
970.672.4342 <tel:970.672.4342>(voicemail)


On Fri, Dec 16, 2011 at 11:03 PM, Hugh Piggott<[email protected] <mailto:[email protected]>>wrote:

   H Dan,

   On 17 Dec 2011, at 00:02, Dan Fink wrote:

    >  parallel connections are BAD with LEDs, and the string with the
   most voltage will eventually fail first, so best practice is
   regulate every string.

   This statement puzzles me so I wonder if you could clarify it for
   me?  If you connect two strings of LEDs (or batteries) together in
   parallel then their voltage will be the same.  So how come you are
   talking about one having more voltage?

   If the answer is that it's absolutely impossible to make the
   connections and leads have the same resistance then this same logic
   applies to two strings that are connected each to its own regulated
   supply.  If a tiny difference in voltage matters (which I doubt)
   then you will have the same issues with a single string.

   What am I missing?

   thanks

   Hugh


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to