Jeffrey,

 

We installed many battery banks in basements for both backup and off-grid 
systems and in the past few years we have gone to battery “rooms” that were 
designed for this type use.  These rooms include fire-rated interior drywall 
construction, an exterior window, a low intake vent louver and a high exhaust 
louver, fire extinguisher, sealed light fixture, and concrete floor and floor 
drain.   Our earlier systems had battery boxes that were sealed and had a 2” 
PVC vent pipe.  Although this size vent seems to work OK, we had lots of 
problems with the outside air being pulled back into the sealed  battery boxes 
due to wind pressure acting on the home, causing a lower pressure inside.   
This of course is not the way this was intended to work!   Also we quickly 
learned that you need good insect screening.

 

Although there is always a danger of a hydrogen gas explosion when dealing with 
lead-acid batteries,  please remember this is near impossible unless the 
hydrogen gets concentrated, so you want to avoid battery locations in confined 
areas having limited ventilation.  Also, a healthy battery bank does not give 
off hydrogen gasses when powering loads or during the large initial bulk 
charging process.   Typically the most potential for hydrogen gas generation is 
during the final “top-off” charge or with a poorly maintained battery bank that 
has low fluid level.   These days we include an in-line PVC mounted 48 VDC vent 
fan controlled by the aux. relay included on almost all battery based 
inverters, which is programmed to start when the battery voltage indicates the 
battery charge is raising.  

 

Jeff Yago

DTI Solar Inc.

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to