Friends:

I have heard, but I have not researched myself, a provision in the code where one could dedicate a panel to be an "AC combiner" to collect the outputs of multiple inverters. You would not install any branch circuit breakers and thereby eliminate the need to comply with the 120% rule. This scenario has never occurred in any projects we have designed, which is why I have not researched the code in this regard.

For a theoretic discussion, however, I wonder this: Even though you have eliminated branch circuits from the equation, you still have the potential to overload the buss bars in or the feeder to the breaker panel in question. If a fault occurs in the panel or feeder, you still have sum of the feeder breaker and the inverter breakers feeding the panel and the feeder in excess of what either is rated for. Is this not a concern? Faults can occur other than in branch circuits, faults such as a wrench dropped across the buss, backhoe fade, defective inverter breaker or compromised insulation. Such a fault could cause catastrophic failure of the panel and/or feeder. Has anyone else pondered this question?

William Miller

PS: I realize a fault in the feeder means that you have fault current below the feeder rating from either direction, but what about at the point of the failure?

Wm



At 09:38 AM 1/22/2012, you wrote:
Hi Nick,

I see (2011) 705.12 (d) where it talks about " supplying branch circuits as the area where it changes.

ie w/o branch circuits then all circuits are protected by the breakers as long as the main buss isn't exceeded by the solar input of course.

But in putting in that metering device plugged into a outlet, now you have a branch circuit and hence the need to comply with 705.12 (D) 2.

But I could be wrong.

jay

peltz power




On Jan 22, 2012, at 8:36 AM, Nick Vida wrote:

That is very interesting Jay, do you have a code reference for no derate needed for your solar accumulation panel?

Thanks,

Nick Vida


btw- Rich, thanks for Bernie Sanders.
_______________________________________________
List sponsored by Home Power magazine

List Address: <mailto:[email protected]>[email protected]

Options & settings:
<http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


No virus found in this incoming message.
Checked by AVG - www.avg.com
Version: 8.5.454 / Virus Database: 271.1.1/4158 - Release Date: 01/21/12 19:34:00

Miller Solar
Voice :805-438-5600
email: [email protected]
http://millersolar.com
License No. C-10-773985
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to