I was just wondering about this same issue: of inverters being used to support the grid. Just as charge controllers reduce their output current as the voltage reaches absorption voltage, I was thinking that GT inverters could do the same thing, instead of just shutting off, and not reconnecting for at least 5 minutes. In Hawaii, with PV penetration on the grid as high as 15%, the utility asks us to widen the voltage operating window beyond IEEE specs, as they've found that when they have a low voltage line condition, the PV systems actually help, and they don't want them to shut off too soon and add to the problem. I could see a new generation of inverter specs beyond UL1741, that was part of a smart grid controlled by the utility. They could extend the operating window when needed to keep the grid more stable. As subsidies dry up, this could be a future selling point, especially if it offered the customer a more stable conditioned power supply. Also be nice for the customer to get paid extra for this emergency peaking capabilities, just like the big generating facilities. It might even make GT w/ battery backup more cost effective, if you could sell some battery amp-hrs at $1/ kwh every once in a while.

Ray Walters

On 2/4/2012 7:05 PM, [email protected] wrote:


Sounds like a voltage source (and sinking) inverter to me.

These types can cause current distortion which the UL1741 / IEEE 1547 specs try to prevent.

Apparent must be able to turn that mode on and off I would imagine. It's not too difficult to do. No wonder
they talk about micro-grids.

The old Trace SW series was a voltage source inverter, even when grid tied and is basically why they had to add that extra inductor box between SW and the grid when selling. It could actually help the grid wave-
form voltage if it was distorted because of non-linear loads.

boB





On 2/4/2012 5:26 PM, Comet Systems wrote:
As I understand the issue they claim to be able to address, the utilities often need a source of reactive power close at the system delivery points, the customer sites, because reactive power does not transmit well through the lines and transformers and uses up transmission resources better used for real power. The reactive power is used as a method of voltage control. Therefore, it is reasonable that the utilities would pay a premium for a reactive power source which would be close to the customers and under their control. The idea has some merit and could be a significant direction for solar pv, but whether an electronic inverter can adequately generate reactive power at will, to act as a compensation device and whether that is the highest and best use for that power source is to be demonstrated. Interesting idea, though.
--
Chris Mason
President, Comet Systems Ltd





_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options&  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules&  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to