If it was connected such that the gen start would disable the DGI inverter and 
any manuel start would use the gen start module the syn would happen.
 
Darryl
 

________________________________
 From: Hilton Dier III <[email protected]>
To: [email protected] 
Sent: Saturday, February 18, 2012 3:12 PM
Subject: Re: [RE-wrenches] AC Coupled
  

Larry,

I have run into similar situations. The simplest thing is to wire
      the Sunny Boy 6000 into a breaker in a small dedicated box on the
      *grid side* of the transfer switch.

Grid present: feeds back normally
Grid absent: interacts with Sunny Islands
Grid absent, genset on: Sunny Boy cut off from the system

I'd assume that they wouldn't lose much, if any production from
      the PV, since they'd probably be running the genset for short
      runs, at night, or in cloudy weather.

Best,

Hilton


 
Wrenches, I have a client with a 4.6 kw grid tied system using a Sunny Boy 6000 
inverter.  We have AC Coupled to that system with 2 Sunny Island 5048's and 
8-Concorde SunXtender 3050T 6 volt batteries in series feeding an essential 
load/critical load sub panel.  The wiring to the sub panel from the Sunny 
Islands is #6, the max wire size that can be used in the AC 1 and AC 2, in and 
out, of the Sunny Islands.  The 2 pole breaker at the sub panel is 70 amps ( 56 
amps feed through current x 1.25 = 70 amps ).
This allow the 4.6 kw solar system and the Sunny Boy 6000 to act as a micro 
grid and charge the batteries and support the loads in the SubPanel when the 
grid is down and still be isolated from the main service panel and the grid.  
We have moved several loads from the main 200 amp service panel into the 
essential load/critical load panel, the well pump, the refrigerator, the 
circulator/boiler controls for the propane fired radiant heating system and 
some lights and communication circuits.   The main 200 amp main service panel 
has an integrated manual transfer switch that has allowed them to fire up the 
gas powered Honda generator and run all of the loads when the grid was down 
before we installed any systems to their home.  They would like to be able to 
continue to do this in an extended power outage. So here is the question?  In a 
power outage, if they fire up the generator and move the manual transfer switch 
in the Main Service Panel to generator, the
 Sunny Islands will see this generator power coming from the Main Service Panel 
and switch from Back Up Mode to Pass Through Mode.  The Sunny Boy 6000 will 
send any excess power not used by the loads to the the generator (as if it was 
a net metering arrangement ) believing it is the grid. This would probably 
destroy the generator or some other disasterous scenario.   So how can the 
generator feeding the Main Service panel be isolated from the Sunny Islands and 
Sunny Boy feeding the SubPanel as a micro grid in a power outage and still 
provide power to the loads that are in the Main Service Panel? Thank you for 
the collective wisdom and knowledge that this group has acquired from years in 
the trenches making it all happen. Larry  

 
-- 
Hilton Dier III
Renewable Energy Design
Partner, Solar Gain LLC   
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to