I am configuring a 50KW roof array and plan to use a 3 phase 50KW central 
inverter.  There are multiple options for the lugs/fusing for the Inverter 
incoming DC conductors.  PV Powered for example offers everything from a single 
set of unfused lugs for the Positive and Negative input up to 5 x 60A fused 
lugs.  My question is if I am using a external fused DC string combiner with 
integrated DC Disconnect and bring the single set of conductors into the 
inverter with the option of 1 set of lugs with no fuses in the inverter what 
protects the large conductors between the fused string combiner/Disco and the 
inverter if there was a problem such as a short on these conductors? 

Any and all feedback is appreciated.