I am not going to name names or firms on this one to protect the guilty, but recently I was called in to commission two different newly constructed bank buildings for a major bank that I am sure you all would know, that recently installed two large solar pv systems. After commissioning the interior equipment, lighting, HVAC systems, ect, I then started to commission the solar systems, but could not find any shop drawings, sizing information, or wiring diagrams for the solar systems which I had received for the other non-solar systems. When I went back to the architect and engineering team that had designed the buildings , I was told neither designed or specified the solar systems that had been installed just after the building's roofs had been completed. I then went to the bank's property manager and made repeated attempts to get this solar information from him since he was the person who managed all new construction and authorized the payments.
Somewhat frustrated in getting no response I finally sent him a very long list of the wiring problems and code violations I had found without the solar design drawings including several very serious fire hazards in the array wiring.. This included exposed multiple USE-2 wires (not smoke rated) running through the attic and nailed to the wood trusses (no metal conduit and no support) , mis-matched inverter to solar array sizing, all under-module roof wiring laying on metal roof surface, multiple array strings stuffed through a hole in attic fan roof curb, emergency dis-connect and emergency labels mounted 18" above ground level and impossible to read standing up, and many more. Expecting a big thank you for telling him his solar contractor was ripping him off, instead I received a real long nasty gram telling me to be a "team player". He also said he did not like my attitude which should be more get-along and not "trying to find fault". Finding out what was wrong was why I was hired !!! I could not understand why he was not calling the fire Marshall or building inspector on this solar installer and demanding they fix this before their banks burn down. Several weeks later I was talking to a design professional who had worked with this same property manager on a prior project and he told me that this property manager had attended one of those one-day solar classes and had then designed the two solar systems himself, he had also ordered all the solar materials over the internet, and wanted to save the bank money by not hiring a solar contractor. I was also told this property manager was actually up on the high lift helping his local electrician friend (who had never installed any solar hardware) to install the roof array on the banks. I am sure if I remained a "team player" for this guy and not demanded that this get fixed or I walk, that this would have started a fire in the attic sooner or later, and after I provided the commissioning while wearing my team member hat. If that had happened, you can bet who would have been blamed. Word to the wise, beware of the one-day solar wonder, especially if they work in a bank! Jeff Yago _______________________________________________ List sponsored by Home Power magazine List Address: [email protected] Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org