The battery enclosure standards that MidNite is listed for is
UL508A 1st edition and CSA-C22.2#14-10, 11th edition
I don't think we have one that will fit this very large size of battery,
but I'm not 100% sure on that.
boB
On 3/22/2012 3:24 PM, Mark Frye wrote:
Is there a Standard to which a battery enclosure can be tested such
that it can be listed and marked as conforming to the requirements of
performance that a battery enclosure must conform to in order for that
battery enclosure to be used as a battery enclosure?
Is the inspector looking at the enclosure as a piece of electrical
system equipment or as secondary containment for the corrosive liquids?
MPF
On 3/22/2012 2:32 PM, Dana wrote:
Jeremy,
If you do not find a Listed enclosure you do not have to provide one.
In other words if it does not exist it cannot be required. I have yet
to hear of one. It was so with wind generators for a long time till
one came out.
Thanks
Dana Orzel - Great Solar Works, Inc - E - *[email protected]* - V
*970.626.5253*
F - 970.626.4140 C - 970.209.4076 web - www.solarwork.com
"Responsible Technologies for Responsible People since 1988"
*/P /**/Please consider the environment before printing this email/**//*
*From:*[email protected]
[mailto:[email protected]] *On Behalf Of *All
Solar, Inc.
*Sent:* Thursday, March 22, 2012 3:16 PM
*To:* 'RE-wrenches'
*Subject:* [RE-wrenches] Listed Battery Enclosure?
Wrenches,
I am looking to install some Surrette dual container batteries. 24-
2v cells and the inspector is looking for a 'listed' enclosure.
Any takes on this?
Jeremy
All Solar, Inc.
Jeremy and Amy Rodriguez
1463 M St
Penrose, CO 81240
www.asolarelectric.com <http://www.asolarelectric.com>
Phone 719-372-3808
Fax 719-372-3804
Email [email protected] <mailto:[email protected]>
Email [email protected] <mailto:[email protected]>
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org