My apologies.  I see this recommendation comes from Magnum.
The suggestion is still valid when other brands are involved and
parallel capacitors are considered. 


Dan


--- On Tue, 3/27/12, Exeltech <[email protected]> wrote:

From: Exeltech <[email protected]>
Subject: Re: [RE-wrenches] Wood boiler ignition issue
To: "RE-wrenches" <[email protected]>
Date: Tuesday, March 27, 2012, 5:11 PM

Adding a capacitor of that size across the inverter's output may cause problems 
for the inverter.  Much depends on how the inverter's output
voltage control loop is designed, among other things.

Before making any changes of this nature, I highly suggest contacting the 
inverter manufacturer to ask them what issues (if any) may result from such a 
modification.

In turn, they may request from you more detail about nature of the load the 
inverter will be powering.  Is it reactive (and if so, what's the power factor)?
 Linear or non-linear? And so forth....  It would be helpful to if you have this
information available before you call them.


Regards,


Dan Lepinski
Senior Engineer
Exeltech

 
--- On Tue, 3/27/12, Brian Faley <[email protected]>
 wrote:

From: Brian Faley <[email protected]>
Subject: Re: [RE-wrenches] Wood boiler ignition issue
To: "RE-wrenches" <[email protected]>
Date: Tuesday, March 27, 2012, 4:04 PM

Hi Kris,  A solution to try would be to add a motor run capacitor across the 
line at the boiler.  10uF-20uf range may improve the crossover distortion 
enough to allow the boiler ignitor to operate properly. Start with 10uF.   
Regards,Brian  Brian FaleyChief EngineerMagnum Energy Inc.2211 West Casino 
RdEverett, WA 98204Ph 425-353-8833www.magnumenergy.com      From: 
[email protected] 
[mailto:[email protected]] On Behalf Of Kristopher
 Schmid
Sent: Monday, March 26, 2012 11:51 AM
To: RE-wrenches
Subject: [RE-wrenches] Wood boiler ignition issue  Esteemed wrenches,I am 
assisting in troubleshooting a stand alone system with three stacked Magnum 
4448 PAE inverters.  The electric ignition of LP for the wood boiler will not 
fire from inverter power.  As soon as we fire up the generator, the boiler 
ignites.  Has anyone seen this before?  Is there a solution?  The boiler is a 
Central Boiler E-Classic 2400.Thanks in advance!----------
Shine On!Kris Schmid
Legacy Solar, LLC
864 Clam Falls Trail
Frederic, WI 54837
715-653-4295
www.legacysolar.com
NABCEP Certified PV Installer
BSEE 
-----Inline Attachment Follows-----

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


-----Inline Attachment Follows-----

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to