Not necessarily. NEC 2008, 250.32 (B), Exception allows you to use the neutral conductor for existing structure so long as several requirements are met.

Check it out.

On 4/11/2012 8:41 AM, Aladdin Solar wrote:
I meant the question largely to be a generic one but I can give you an example: Buried conductors are 6AWG. No additional grounding conductor exists between the main and detached building. As Brian Mehalic already responded, the 60A subpanel would tough to deal with for inverter sizing. Assume the AC disconnect is required near the main meter and so would have to disconnect all circuits in the subpanel. So say we put a 50A main breaker in the 60A subpanel to allow a Fronius IG 3.0 (3000 watt) and a string of 12 Sharp ND240s or similar. The PV ground would have to hit a ground rod at the garage and a grounding conductor would need to be buried back for bonding at the main building--right?
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to