Wrenches,

Good points.
To recap: Max recommended strings in parallel on cyclic applications is 1 to 3. 
 More than 3 strings in parallel will over time promote unbalanced charge of 
the strings. Unbalanced charge will promote sulfatation (lead sulfate crystals 
hardening) of the plates on the units not getting enough charge, and, promote 
corrosion (due to loosing water) & possibly thermal challenges on the “boiling” 
overcharged units, while accelerating batteries ageing on all.

In addition to the issue of the max number of strings in parallel, batteries 
need to see full charge (system design) to stay in good health. FLA batteries 
need to see equalization when the S.G delta between cells are reaching 30 
points difference. Equalization on FLA batteries addresses S.G. unbalance and 
acid stratification, both of which are challenging the battery health.

John
Trojan Battery Company

From: [email protected] 
[mailto:[email protected]] On Behalf Of Drake
Sent: Friday, April 13, 2012 9:41 AM
To: Darryl Thayer; RE-wrenches
Subject: Re: [RE-wrenches] Hot Trojan Batteries

I've seen batteries get very hot from deficit charging, where batteries are 
cycled rapidly and never fully charged.


At 10:15 PM 4/12/2012, you wrote:

I have seen very hot batteries infact batteries that melted.  and caught fire.  
the problem was that the string was several strings in parallel, and one of the 
strings had thermal runaway.  during charge one battery got hot, and it has 
lower voltage and gets more current. then it get hotter because of the more 
curent. soon it is so hot the other batteries start to discharge through the 
hot battery.

A similar event will occur when one battery in a string of batteries develops a 
bad cell, and the othe batteries in parallel strings will force current 
backwards through the cell.  and thermal runaway occcurs in the hot battery.

From: Jason Szumlanski <[email protected]<mailto:[email protected]>>
To: RE-wrenches 
<[email protected]<mailto:[email protected]>>
Sent: Monday, April 2, 2012 11:53 AM
Subject: Re: [RE-wrenches] Hot Trojan Batteries

There must be some confusion here about the charging rate. C/20 refers to 
capacity divided by 20, so in the case of a 325aH battery (capacity @ the 20 
hour discharge rate) we’re talking about charging at a 16.25 amp rate. I’m 
sure John is not referring to a maximum rate of 10-15% of 16.25 amps, but 
10-15% of the 325aH capacity.

Jason Szumlanski
Fafco Solar


From: 
[email protected]<mailto:[email protected]>
 [ mailto:[email protected]] On Behalf Of John DeBoever
Sent: Monday, April 02, 2012 12:14 PM
To: [email protected]<mailto:[email protected]>; RE-wrenches
Subject: Re: [RE-wrenches] Hot Trojan Batteries

Jeremy, Wrenches,

165°F is definitely too high and you should stop immediately any charge to 
avoid further major problems. I recommend you contact our Trojan Tech Support 
for help at 
http://www.trojanbatteryre.com/Tech_Support/Tech_Support.html?tab=0#TabbedPanels1#top<http://www.trojanbatteryre.com/Tech_Support/Tech_Support.html?tab=0#TabbedPanels1top>

Below are few perspectives to help the diagnostic:

o   System issues:
ü  Check Charger setting: the C/20 rate mentioned is definitely too high and 
will damage the battery. The maximum recommended current rate is 10-15% of C/20 
for a deep-cycle flooded lead acid battery. Other C/rates are possible but are 
application specific and not typical.
ü  Check Voltage settings: these are provided on Trojan datasheets, see here: 
http://www.trojanbatteryre.com/Tech_Support/literature.html
ü  Check Temperature compensation: -0.028VPC for every 10°F above 77°F (add 
0.028 VPC for every 10°F below 77°F or subtract 0.020VPC for every 10°F 
above 77°F. See here: 
http://www.trojanbatteryre.com/PDF/Signature_Trojan_ProductLineSheet.pdf
ü  Check Voltage sensor status and connection. Dedicated wiring is recommended
ü  Check temperature sensor. It shall be well positioned, typically in the 
middle of the battery bank at the warmest point.
ü  Check if air circulation between the battery units.
ü  Check if adequate air ventilation of the battery room.

o   Battery issues:
ü  C/20 charging rate is too high (see above)
ü  How old are the batteries? Ageing batteries will face micro-shorts that 
will decrease the battery turnaround efficiency over time that translates in 
higher temperature generation. Typically the battery temperature range is about 
20oF above ambient temperature, and typical min and max limit are -4°F to 
113°F.
See here: 
http://www.trojanbatteryre.com/PDF/Signature_Trojan_ProductLineSheet.pdf
165°F is way too high and will damage the units
ü  Maybe you are facing one or more shorted units: check the voltage and it 
will quickly indicate if a unit is shorted.  Shorted units will generate heat 
and will jeopardize the charging of other units. Remove shorted units and 
consult tech support your charger supplier if possible to reconfigure of your 
battery bank with fewer units, configured at a lower battery bank voltage, 
using same voltage settings recommended by Trojan Battery Company.  Typically 1 
to 3 units less would be acceptable, depending the charger manufacturer 
settings.
ü  Maybe you are facing sulfated batteries, resulting from low charging, thus 
resulting in lower overall turnaround efficiency. This will heat some healthier 
units of the battery bank, accelerating corrosion damages. The max temperature 
acceptable being 113°F, please consult Trojan Tech Support: 
http://www.trojanbatteryre.com/Tech_Support/Tech_Support.html?tab=0#TabbedPanels1#top
ü  Please deal directly off-Wrenches list, with Trojan Tech Support for better 
fine tune resolution: 
http://www.trojanbatteryre.com/Tech_Support/Tech_Support.html?tab=0#TabbedPanels1#top

I hope this help,

John
John F. DeBoever
Global Technical Director – Renewable Energy
Trojan Battery Company

12380 Clark Street
Santa Fe Springs, CA 90670
Tel: +1-562-236-3000 Ext. 3139
Cell: +1-845-514-7600 – NY office time zone: USA EST (GMT-5)<
Skype: john.f.deboever
Fax: +1-562-236-3239
[email protected]<mailto:[email protected]>
www.trojanbattery.com<http://www.trojanbattery.com/>

-----Original Message-----
From: 
[email protected]<mailto:[email protected]>
 [ mailto:[email protected]] On Behalf Of 
[email protected]<mailto:[email protected]>
Sent: Sunday, April 01, 2012 7:20 PM
To: [email protected]<mailto:[email protected]>
Subject: [RE-wrenches] Hot Trojan Batteries

Wrenches,
Can anyone explain why an L16 bank would be at 165F at rest.  Over a C20 charge 
rate, but I have a feeling there might be an internal short

Jeremy
All Solar
Sent via BlackBerry. Sorry for typos and shorthand!
_______________________________________________
List sponsored by Home Power magazine

List Address: 
[email protected]<mailto:[email protected]>

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>



This e-mail message and any attachments that accompany it may contain 
information that is confidential, privileged, or protected from disclosure. It 
is intended solely for the use of the individual(s) to whom it was intended to 
be addressed. If you have received this e-mail by mistake, or you are not the 
intended recipient, any reading, disclosure, copying or other use of this 
communication is strictly prohibited. If you have received this communication 
in error, please immediately advise the sender at their phone number listed 
above, or by electronic mail, and also permanently delete the original and all 
copies of this e-mail and any attachments from all locations. Thank you.

_______________________________________________
List sponsored by Home Power magazine

List Address: 
[email protected]<mailto:[email protected]>

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org/>



_______________________________________________
List sponsored by Home Power magazine

List Address: 
[email protected]<mailto:[email protected]>

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org/>

Drake Chamberlin
ATHENS ELECTRIC LLC
OH License 44810
CO license 3773
NABCEP Certified PV

This e-mail message and any attachments that accompany it may contain 
information that is confidential, privileged, or protected from disclosure.  
It is intended solely for the use of the individual(s) to whom it was intended 
to be addressed. If you have received this e-mail by mistake, or you are not 
the intended recipient, any reading, disclosure, copying or other use of this 
communication is strictly prohibited.  If you have received this communication 
in error, please immediately advise the sender at their phone number listed 
above, or by electronic mail, and also permanently delete the original and all 
copies of this e-mail and any attachments from all locations. Thank you.
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to