Jason,

690.31(A) permits PV wiring for circuits below 30 volts to be installed in accessible locations without conduit or raceways. But 690.31(E) requires the use of metal raceways for PV circuits inside a building. It does not require EMT. It specifically allows MC cable. Unless there are local codes specifying otherwise, MC cable should be allowed. Even that is overkill for a small 12-volt module.

Kent Osterberg
Blue Mountain Solar, Inc.
www.bluemountainsolar.com


On 5/3/2012 9:34 AM, Jason Szumlanski wrote:
I'd like some help with code references for an inspector that is requiring EMT for a 12V PV panel that runs a solar water heating circulation pump. The wiring is run through the attic and down to the pump near the water heater. I've never ran into this before (but I have run into this inspector). :)

Jason Szumlanski
Fafco Solar