Eventually all batteries wear out but that is no reason to give up on them 
because the grid is coming in.  It sounds like he simply wants to continue 
using his off-grid system and let the grid take over if the modules can't keep 
up with the demand.  If you're using outback inverters simply program them for 
HBX mode.


David Lauzon
Northern Arizona Wind and Sun Phone-928-526-8017 / 800-383-0195 
Fax-928-527-0729 
Website-http://www.solar-electric.com

----- Reply message -----
From: [email protected]
To: "RE-wrenches" <[email protected]>
Subject: [RE-wrenches] Off-Grid to Grid-Connected -essential loads
Date: Fri, May 4, 2012 6:23 pm
IMHO, the batteries are the real skeleton in the closet here. Sooner or later 
they're gonna poop. at 2400 Ah you're likely running a multi string set up, so 
it's likely someone's number is already on the board. Even if you set the FX 
down to a trickle charge or use some kind of contactor to fake the FX into 
thinking the grid is really a gen set, sooner or later the batteries will fail. 
Better to design for it now.. Besides, Rather than regulating solar input to 
protect batteries, You're better off selling (Storing) power on the grid. 
Depending on the age of the batteries or the competence of the operator (Home 
Owner), I'd either swap out the FXs for a GVFX  (and down size the batteries 
when they puke), or loose the current setup all together and go for a 
batteryless Grid Tie inverter. (and maybe keep the current setup as a whole 
house UPS.. until the batteries poop). Again, depending on the customer, you 
might milk these batteries by setting up individual strings on an isolation 
switch (like in the marine industry), at least this way you can referee. Good 
Luck. db



Dan Brown
Foxfire Energy Corp.
Renewable Energy Systems
(802)-483-2564
www.Foxfire-Energy.com
NABCEP #092907-44




-------- Original Message --------

Subject: [RE-wrenches] Off-Grid to Grid-Connected -essential loads

From: benn kilburn <[email protected]>

Date: Fri, May 04, 2012 5:08 pm

To: Wrenches <[email protected]>



Wrenches,I have an off-grid client who is going to be connecting to the grid.  
Since the system (~9 kW of PV and ~2400 Ah battery) is already well suited for 
the loads, I am wondering about the necessity of an essential loads panelboard. 
 I'm not sure if I see the need since the battery is already sized for all the 
existing loads.
The intent is to continue running all the loads from the battery and have the 
(Outback) settings so that the grid is only used when the PV isn't able to 
maintain a particular battery voltage setting.  
Comments, insights into this type of set-up?
Thanks,benn
DayStar Renewable Energy Inc. www.daystarsolar.ca780-906-7807 Certified 
Construction Electrician Solar Photovoltaic Systems CertifiedCertificate # 
0007SHAVE A SUNNY DAY  _______________________________________________

List sponsored by Home Power magazine



List Address: [email protected]



Options & settings:

http://lists.re-wrenches.org/options..cgi/re-wrenches-re-wrenches.org



List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org



List rules & etiquette:

www.re-wrenches.org/etiquette.htm



Check out participant bios:

www..members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to