James and all, Sorry to hear my time in Hawaii did "no good." I think I'll quit....
Seriously though, the discussions in several of my Hawaii workshops centered around "load-side" taps, not line-side service connections (don't like to call them taps). A tap is a type of connector. Since we did not discuss line-side connections much, I can understand how it didn't help. There is a lot of misunderstandings about these types of connections. If you have a 100-amp service, then your PV system is only limited by the size of the service conductors. An 80-amp continuous PV inverter could be connected through a 100-amp OCPD into a 100-amp feeder upstream of the first overcurrent device provided a legal, listed connection could be made at that point. If the meter base or service panel does not have a means to make this connection (as pointed out in detail in previous posts), a junction box could always be installed upstream of the service panel to make a connection. AHJs may reject this idea, but it is only because they don't understand it or it hasn't been explained properly. Bill. -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Dave Click Sent: Monday, May 21, 2012 5:46 AM To: [email protected] Subject: Re: [RE-wrenches] Line side taps in Hawai'i Square D probably has a similar "solar-ready" panel; I remember seeing some monster (4' tall? they were big) Cutler Hammer panelboards at SPI 2010 that had it too. On my house I have a Square D RC2M200S which has simply a 200A main plus a 2P 50A breaker (perfect for PV). This is a much smaller enclosure (18"H x 20"W) than some others I've seen, but with limited functionality; no load breakers can be added here which can be a problem when using it in a retrofit. This is an issue for the combination service entrance devices as the conductors from the utility meter load terminals to the main breaker are factory-installed and can't be touched. I did an inspection two years ago where the installing contractor's solution was to interconnect the PV on the utility side of the meter. This is not a solution. If the issue is that "nobody is allowing line side" connections then you're sorta stuck. As for why the AHJ wouldn't allow it, they should be willing to share their justification with you! If the issue is as Jeffrey's encountered-- they're requiring listed enclosures where line-side connections are made-- then you can get around it either with these Milbank dual lugs http://www.milbankmfg.com/products/Catalogs/CatalogFiles/PDF/K4977.pdf#Tap%2 0Connector or the aforementioned Cutler Hammer or Square D panels. It may be that they've heard about the "listed enclosure" requirement and naively generalized it beyond code requirements. If they're asking for service upgrades, then perhaps they're thinking that a 200A service + 100A PV requires a 300A service-- if it's not battery backup, a simple power flow diagram may prove to them that a 200A service is perfectly adequate. On 2012/5/19 17:52, JRQ wrote: > I had a similar problem working in San Diego. SDG&E insisted that no > taps could be performed in an enclosure unless the contractor could > supply documentation that the enclosure was specifically listed for a > tap, or if an electrical engineer supplied stamped drawings of the tap. > I never did a project that warranted hiring an engineer, so I don't > know what they were looking for there. > > I heard that Square D (or maybe it was one of the other companies) has > a new "solar-ready" service panel with a lug on the line side for a > solar input. You could use the same feeders and service size with a new panel. > > Jeffrey Quackenbush > NABCEP certified PV installer > Peripatetic Solar Technician > > ---------------------------------------------------------------------- > -- > *From:* James Rudolph <[email protected]> > *To:* RE-wrenches <[email protected]> > *Sent:* Wednesday, May 16, 2012 10:48 PM > *Subject:* [RE-wrenches] Line side taps in Hawai'i > > Aloha Wrenches, > > I have recently started working in Hawaii on the island of Oahu and > have run into some interesting problems with the AHJ's. The biggest > issue is nobody is allowing line side taps on the island, so most of > are larger systems are requiring service upgrades, this also requires > replacing the feeder of course and plenty of trenching which adds so > much time and cost to the whole process.. Now I know Bill Brooks was > on island recently and and this seems to have done no good. I was > wondering if anybody can shed some light on this issue and the reasons > why they would not allow this code compliant option. This is allowed > on commercial systems here just not residential to be clear. > > And If your out there Bill, do you have any suggestions on how to > approach this matter with the local inspectors??? > > Mahalo, > > -- > * > James B Rudolph* > *Heleakala Solar* * > * > *Director of Construction* > *NABCEP Certified PV Installer* > * > * > * > * > * > > *Don't get me wrong: I love nuclear energy! It's just that I prefer > fusion to fission. And it just so happens that there's an enormous > fusion reactor safely banked a few million miles from us. It delivers > more than we could ever use in just about 8 minutes. And it's wireless! > - William McDonough > > > _______________________________________________ > List sponsored by Home Power magazine > > List Address: [email protected] > <mailto:[email protected]> > > Options & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out participant bios: > www.members.re-wrenches.org > > > > > > _______________________________________________ > List sponsored by Home Power magazine > > List Address: [email protected] > > Options& settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > > List rules& etiquette: > www.re-wrenches.org/etiquette.htm > > Check out participant bios: > www.members.re-wrenches.org > _______________________________________________ List sponsored by Home Power magazine List Address: [email protected] Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org _______________________________________________ List sponsored by Home Power magazine List Address: [email protected] Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org