I would check each string.  I have seen many failed 120 watt Kyocera modules. 
They had a delamination problem.
David Katz

Sent from my HTC smartphone on the Now Network from Sprint!


----- Reply message -----
From: "Eric Stikes" <[email protected]>
To: "RE-wrenches" <[email protected]>
Subject: [RE-wrenches] Troubleshooting Off-grid PV
Date: Sun, May 27, 2012 2:51 pm



Hi Wrenches,

I inherited an off-grid PV system that seems to be significantly under 
producing. I have:

12 KC120's (~17V 7A each) paired up 2 in series, for 6 strings terminated on 
new 15A breakers in a new Midnite combiner,
Output of combiner passes through a 60A breaker then into a SolarBoost 50 
charge controller. An SW4024 ties in the CC, a Kohler 8.5 Gen set, and a Yuasa 
24V battery bank.

My problem is that I never see more than about 5A (displayed at charge 
controller) coming off the array, even in full sun, regardless of the state of 
charge of the batteries. I figure I should see, at least once in a while, 
closer to between 20-30A. Batteries are, admittedly, passed their life 
expectancy as the system was installed in '02 and I am sure this is part of the 
problem. I'm thinking that if the batteries are at about 1/2 capacity (don't 
own a hydrometer...yet), the controller senses the batteries are near full SOC 
even at lower voltage (~24V) and is therefore attempting to trickle charge even 
in the bulk stage. Though this is not how the CC is supposed to function in 
bulk, obviously, I'm assuming the old batteries are altering the standard 
operating conditions of the system. I've adjusted the Bulk set point on the CC 
but that doesn't seem to make a difference.

I doubt this is part of the problem but the generator is problematic as well 
(it has it's own array of maladies).

Any insight is greatly appreciated. Thanks!

--
Eric Stikes
Owner
SunHarvest Solar
+1 (530) 798 - 3738
www.harvesthesun.com<http://www.harvesthesun.com/>
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to