I have done this with two houses, each having its own utility meter and 
service. The AHJ approved it because all of the solar components were exterior 
to the host building, we had DC and AC disconnects at the host building, and we 
had engraved placards at both services identifying the location of everything 
and the point of interconnection. I don't believe there is anything in the NEC 
that would disallow it, but local codes or utility requirements might be a 
problem.

-Hans 

On Jun 15, 2012, at 5:49 PM, Allen Frishman <[email protected]> wrote:

> Hey Wrenchers,
> I have been asked to participate in a feasibility study for a ~300KW Grid 
> Tied solar system in NYC.  There are two adjacent detached buildings,  one 
> has great unshaded space with very little usage and the other has no 
> available roof space with high annual usage.   The separate owners of the two 
> buildings want to work out a deal to install the array on the good space roof 
> and grid connect to the other building.  Is there anything in the NEC that 
> will not allow this?   I know there was a topic discussed last year "Two 
> Buildings, two services, one roof" but that project was never installed and 
> therefore no conclusion made.  
> 
> Any and all feedback is appreciated.
> 
> Thank you
> Al Frishman
> AeonSolar
> 
> (917) 699-6641 - cell
> (888) 460-2867
> www.aeonsolar.com
> 
> 
> Al Frishman
> AeonSolar
> 
> (917) 699-6641 - cell
> (888) 460-2867
> www.aeonsolar.com
> 
> 
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: [email protected]
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to