I would use a 200A sub panel with 8 x 25A breakers to accumulate the PV output, as I doubt you could install 8 3Ph breakers in your main panel, and why would you want to? You shouldn't need to observe the 120% rule for the main breaker on the main panel as there are no loads. Same for the panel rating. The main panel would need a 200A breaker for the PV input and 120% comes into play. Be careful that breaker is rated as bi-directional.
Chris On Mon, Jun 25, 2012 at 10:39 PM, Jesse Dahl <[email protected]> wrote: > > All, > > I'm looking for ideas on the electrical integration of the following > system: > > 800A service > PV system employing enphase 215W inverters broken down into 8 output > circuits. Each circuit will be 208V 3 phase 20A. > > The question is on how to grid tie this. My first thought is a sub panel > for PV intertie only. I saw a similar diagram on the enphase website, > using 5 circuits and a 125A panel.... > > What are people doing in situations like this? > > Thanks as always. > > > Jesse > Sent from my iPad!!! > _______________________________________________ > List sponsored by Home Power magazine > > List Address: [email protected] > > Options & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out participant bios: > www.members.re-wrenches.org > > -- Chris Mason President, Comet Systems Ltd www.cometenergysystems.com Cell: 264.235.5670 Skype: netconcepts
_______________________________________________ List sponsored by Home Power magazine List Address: [email protected] Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org