Chris,

SCRs are capable of creating voltage spikes that cause noise well into the radio frequencies. But with TWACS there is an inductor in series with the SCR that is tuned such that the pulse caused when it fires is 0.5 ms to 1.0 ms wide with very little high frequency content. Because the frequency content is very low, it difficult to filter out. Ferrite toroids are of no help and large capacitors will prevent the utility from reading the meter too. The pulse location is near the zero crossing so it makes for a dirty looking waveform for about 8 seconds while the meter is sending data. Never-the-less, it's actually easy to make a reliable frequency measurement by shifting the measurement threshold off zero far enough that the TWACS signal doesn't interfere. The Enpase folks should be able to do that with a firmware change.

Kent Osterberg
Blue Mountain Solar, Inc.
www.bluemountainsolar.com
t: 541-568-4882

On 7/8/2012 4:47 PM, Chris Mason wrote:
Kent,
I haven't any direct experience with the smart meters tripping inverters, but the issue of SCRs and generators is well known. I suspect you understand the problem, but to recap it, the problem revolves around the way SCRs make a sine wave. A motor driven generator controls the alternator output by increasing or decreasing the DC excitation level. It does that by sensing the "zero crossing", or point in the sine wave at which the voltage is zero. This happens 120 times a second on a 60Hz system. When the source of the electricity is electronic, the waveform will sometimes be messy around the zero crossing. That gives the voltage control circuit problems to detect the zero crossing We see this a lot when trying to drive a UPS from a generator, it can drive the generator crazy.

I suspect your problem is the same. The SCR in the meter disturbs the waveform and the inverter thinks it is a faulty waveform. I would try a low pass filter between the meter and the inverter. A properly sized capacitor ought to remove any noise above 60hz and present a clean waveform to the inverter.


On Sun, Jul 8, 2012 at 7:06 PM, Kent Osterberg <[email protected] <mailto:[email protected]>> wrote:

    Wrenches,

    There weren't very many replies to my question about
    grid-connected inverter compatibility with utility remote meter
    reading systems so I'll explain my recent experience with hope
    that this information may be of assistance sometime.

    Last fall I installed an Ephase system for a customer. Soon after
    it was on line he complained that the inverters were dropping off
    line frequently. Since we had a lot of cloudy weather in northeast
    Oregon all winter, it wasn't easy to see what was going on. In the
    spring we had some clear days and noticed that the inverters were
    dropping off line several times a day at exactly the same time
    every day. It didn't take very long for our suspicion to turn to
    the utilities new remote meter reading equipment. Because our
    weather has been so cloudy it took a while to find clear days
    where the utility could provide assistance. But with their help by
    reading the meter on demand and temporarily disabling the meter
    communications we were able to finally prove the remote meter
    reading system is tripping the inverters offline for five minutes
    every time the meter sends a data packet.

    Recently the remote meter reading system has expanded to more
    areas so we have now observed this problem with both Enphase M190
    and M215 inverters. The system we've observed that is in town is
    seeing many more dropouts, so we think every kWh meter on the same
    service transformer and maybe some beyond it are causing trouble too.

    The remote meter reading equipment is made by Aclara and uses
    their TWACS technology. This isn't new technology and with more
    remote meter reading systems going in all the time there will be
    more occurrences of incompatibility. Certainly more between
    Enphase and TWACS. And possibly more between other inverters and
    other communications systems.

    At present I'm really dissatisfied with Enphase's support on this
    issue. All they've done is point out that only a few systems have
    been affected and put us in the position of telling customers that
    they'll just have to live with the lost production time. Until
    Enphase comes up with a fix, I won't install any more Enphase
    inverters.

-- Kent Osterberg
    Blue Mountain Solar, Inc.
    www.bluemountainsolar.com <http://www.bluemountainsolar.com>
    t: 541-568-4882 <tel:541-568-4882>

    _______________________________________________
    List sponsored by Home Power magazine

    List Address: [email protected]
    <mailto:[email protected]>

    Options & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>




--
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com <http://www.cometenergysystems.com>
Cell: 264.235.5670
Skype: netconcepts



_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to