Allan's point is well taken.

Resistive connections within the PV could easily be another cause for
excessive DC-side voltage drop, and clearly merits closer examination.

Dan


--- On Sun, 7/22/12, Allan Sindelar <[email protected]> wrote:

From: Allan Sindelar <[email protected]>
Subject: Re: [RE-wrenches] Low power production at a winery: DC voltage drop 
upon SB6000 start-up
To: "RE-wrenches" <[email protected]>
Date: Sunday, July 22, 2012, 12:25 PM


  

    
  
  
    Eric,

      Without challenging any of Dan's calculations, I will add that the
      BP SX170 has proven to be prone to failures. You didn't indicate
      which model of BP170 you have. I think that the SX170s are the
      model that was the source of BP's conditional recall of modules
      that could cause roof fires - no, I'm not making this up, but
      neither is my memory sharp about this. 

      

      Here's the text of an email dated 10/10/07 from Phil Undercuffler,
      now at Outback, then at Conergy:

      
         
BP reports that these failures tend to manifest early in the product
life; modules that will have problems will generally fail in the first
few years of service.  Failure rates are reported as .02% of product
distributed in US, .03% in European market
 
Cause:  
The solder joint inside the low-profile potted J-box on MC connected 
modules is what is failing.  

Changes in solder formulation (due to the phase out of lead solder 
for environmental reasons) and move to heavier gauge wire made it
harder to make a good solder joint.  

Failure of the solder joint causes heating and arcing, which can in 
certain cases ignite the epoxy material surrounding the joint.   

BP's concern is the potential for the burning epoxy to ignite 
flammable materials in the close vicinity of the junction box.  

BP does not believe that standard roofing materials such as asphalt 
shingles, tile or metal roofs will be affected by this issue.  

A dealer can perform tests with a relatively inexpensive infrared 
thermometer or contact thermal probe.  It is best to measure the 
module from the front, while in operation.

Problem modules will show 10-20 C difference between the solder 
joint and the module field just before failure.  
 
 
For solder connection, gather the following info:
Measure VOC and ISC
Physical examination, looking for brown or black spots on
solder traces
Model number
Serial number
      
      

      They are rated at +/- 9%, one of the worst specs around at that
      time. We used quite a few of them at that time and have replaced
      many of them under warranty, including one entire 40-module
      commercial array, identical to the one you described.

      

      I would still encourage testing individual string outputs for Vmp
      and Imp under load, to look for significant variances. At worst,
      it gives you a baseline reading. Also, if you can, look for
      browned hot spots, visible beneath he glass in the area over where
      the leads leave the module back. 

      Allan

      

      
        
        
        Allan Sindelar

        [email protected]

          NABCEP Certified Photovoltaic
            Installer

            NABCEP Certified Technical Sales Professional

            New Mexico EE98J Journeyman Electrician

            Founder and Chief Technology Officer

            Positive Energy, Inc.

            3209 Richards Lane (note new address)

            Santa Fe, New Mexico 87507

            505 424-1112

            www.positiveenergysolar.com 
        


            
        

         
      On 7/22/2012 10:56 AM, Exeltech wrote:

    
    
      
        
          
            Eric,

              

              I checked my magic spreadsheet for the BP SX170.

              

              Using 800W/m^2 irradiance, and a presumed ambient of 37C
              (98F),

              everything appears to be working within specified
              tolerances.  The

              presumed conditions create exactly your measured Voc,
              which is

              why I used them.  Other temperature and irradiance
              combinations

              will also work...

              

              The voltage delta you measured between Voc and Vmpp is
              within

              BP's specifications.  No PV has a perfect "fill factor". 
              Fill factor is the

              aspect that determines the shape of the V/I curve
              established when

              Voc and Vmpp are plotted.  The BP you mentioned have a
              fill factor of

              0.769, which is very typical of polycrystalline PV.  A
              perfect fill factor

              would be 1.0 (Vmpp equal to Voc), which obviously doesn't
              happen.

              Thus, all PV have an operating voltage at maximum power
              that's below

              the open circuit voltage -- some more than others.

              

              

              Measured:

              375Voc

              280V at inverter at mpp

              14-15A (fluctuating) at mpp

              

              Calculated:

              375Voc

              301V mpp

              14.96A mpp

              

              Assumed:

              800 w/m^2

              37C (98F) amb

              

              4,503W array power under above conditions

              

              280V measured at the inverter

              14.5A

              

              Presuming 301V is correct Vmpp, this equates to:

               

              1.38 ohms total system R, and 290W loss

              

              290W/4503W = 6.44%

              

              6.44% total loss --higher than a 2.5-3% best-practices
              target, and likely

              due to slightly oxidized and/or loose connections in the
              DC-side of the

              system.  Could also be due to long conductor runs,
              slightly undersized

              conductors for the amperage and length, or both.

              

              As Jeff Quackenbush mentioned, Vmpp is slighly lower than
              one might

              expect, but doesn't appear to rise to the level of
              something that would

              yet be indicative of something wrong.

              

              

              Dan

              

              

              

              

              --- On Sat, 7/21/12, SunHarvest <[email protected]>
              wrote:

              

                From: SunHarvest <[email protected]>

                Subject: [RE-wrenches] Low power production at a winery:
                DC voltage drop upon SB6000 start-up

                To: "RE-wrenches"
                <[email protected]>

                Date: Saturday, July 21, 2012, 3:19 PM

                

                
                  
                  
                    Hello Wrenches,
                     
                    I am helping a
                        client troubleshoot a complaint about
                        underproduction of his on-grid system installed
                        about 6-8 years ago. At first I thought I might
                        encounter the bad Kyocera KC120 issue but it
                        turns out they have BP170's, 40 of them for an
                        STC power rating of 6.8kW. 
                     
                    Ratings of the BP
                        modules: PTC=150.7, Vmp=35.4, Voc=44.2, Imp=4.8,
                        Isc=5
                     
                    The system has four
                        panels of ten modules wired in series for a
                        nominal rating of about 350v, 4.8a per string.
                     
                    At the DC
                        disconnect (first accessible combiner) I
                        measured: All strings right at about 375v(oc),
                        4.7a(mp). After the strings are combined, at the
                        DC input of the SB6000 (with the AC power to the
                        inverter OFF) I measured about 375V as expected.
                        Once the AC power is connected, the
                        SB6000 starts up, and MPP operation is
                        initiated, the DC voltage drops to about 280V,
                        and amps sit between 14 & 15A.  I didn't
                        think the voltage was supposed to drop upon MPP
                        tracking...especially this much. This voltage
                        drop would account for the observed power loss
                        between actual and rated production values. I'm
                        going to check with SMA but I wanted to ask the
                        experts here too, as someone may advise
                        something like, "Oh yeah, BP modules have a
                        similar defect as the Kyocera..."
                     
                    My questions:
                     
                    Is the DC voltage
                        supposed to drop significantly in MPP mode on
                        these inverters?
                    If not, does this
                        indicate a bad inverter?
                    

                        Anyone know of problems with BP modules
                        manufactured around 2006-2008?
                     
                    The Kyocera modules
                        showed good volts and amps until a load was
                        connected. Seems like a similar issue here.
                     
                    Eric Stikes

                        SunHarvest Solar

                        A Sustainable Energy Group Partner

                        +1 (530) 798 - 3738

                        www.harvesthesun.com
                  
                
                

              
            
          
        
      

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to