Thanks David, I was in residential mode and just saw the 240V listed in the OCPD table!

On 2012/8/30 16:47, David Brearley wrote:
I'm assuming it's a balanced 3-phase interconnection, which fits with the 
reported phase current of 42 A:

(3 x 5000 W) / 208 V / 1.73 = 41.7 A

Or more simply:

24 A per inverter x 1.73 = 41.5 A

However, no one reviewing a single-line should have to guess about the service 
type....

On Aug 30, 2012, at 3:12 PM, Dave Click wrote:

I've seen that one a lot, too. And not to quibble, but the 1-line depicts this 
correctly (no inline fuse shown in the inverter DC disconnect box), though 
there should be a note making this more explicit.

Speaking of sunny days turning off the system, how about the 3 30A inverter 
breakers' combined feed going into a 55A breaker. Also... a 55A breaker? 
Really? I guess the designer wanted to leave a little headroom to avoid scaring 
the 60A disconnect.

DKC

On 2012/8/30 14:35, Andrew Truitt wrote:

Ahh yes, the old "combine strings before landing on a fused DC input
terminal" trick.  Sure to blow the fuse the first sunny day.  This is
why SMA created their fuse-bypass DC input terminal.  I take it the
installer was not aware of this...



For a brighter energy future,


Andrew Truitt
NABCEP Certified PV Installerâ„¢ (ID# 032407-66)____

Principal
Truitt Renewable Energy Consulting____

(202) 486-7507 <tel:%28202%29%20486-7507>____

http://www.linkedin.com/pub/andrew-truitt/8/622/713



"Don't get me wrong: I love nuclear energy! It's just that I prefer
fusion to fission. And it just so happens that there's an enormous
fusion reactor safely banked a few million miles from us. It delivers
more than we could ever use in just about 8 minutes. And it's wireless!"

~William McDonough






On Thu, Aug 30, 2012 at 11:53 AM, Jason Szumlanski <[email protected]
<mailto:[email protected]>> wrote:

    I was sent to look at another contractor's work, and found three
    SB5000 inverters with blown string input fuses. I was able to
    determine the reason pretty quickly, and was later sent the original
    1-Line, which was installed per the drawings. The 1-Line came from a
    "leading system integrator" who shall remain nameless.

    See anything wrong?

    https://www.sugarsync.com/pf/D6539806_8669786_010829

    Just goes to show you - the contractor needs to take responsibility
    and verify the specifications are correct, safe, and code compliant.

    Jason Szumlanski
    Fafco Solar

    _______________________________________________
    List sponsored by Home Power magazine

    List Address: [email protected]
    <mailto:[email protected]>

    Options & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>





_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to