The four poles of ten modules in each row are each a separate string, combined 
at a fused DC combiner on the west most pole.  A 1 inch PVC conduit runs down 
each pole directly to a buried hand hole box at the west pole of each row.  
Each conduit contains a #8 EGC along with the current carrying conductors.  In 
the hand hole boxes the four #8 wires are irreversibly spliced to the bare #6 
that is laid in and runs the length of the 39 foot trench connecting the four 
poles.  An acorn attaches the bare #6 to a ground rod at each end.  The #8 EGC 
at each pole is irreversibly spliced to the EGC from the rails, rack and pole, 
each of which have lay in lugs.  The module are grounded to the rails with 
WEEBs.  We're following Burndy's paper on how to ground DP&W top of pole mounts.

The #6 should not have any tight bends, it should just leave the hand hole box 
and go in a straight line 39 feet east in the bottom of the trench.  This, 
combined with each pole being 5-7 feet into the ground should be sufficient 
grounding, I'd have thought.  It's about 100 times more surface area than the 
average house with a single ground rod.

Jeff
Hudson Solar

From: [email protected] 
[mailto:[email protected]] On Behalf Of Larry Crutcher, 
Starlight Solar Power Systems
Sent: Friday, September 07, 2012 11:54 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Extensive Lightning Damage to Modules

Hello Jeff,

I am curious about the network of ground rods and #6 wire. Can you describe how 
the modules and mount are connected to this ground system?
Are there any tight bends anywhere in the #6 wire?
Are any of the poles or mounts connected to other poles/mounts before going to 
the ground system?
Are any PV wires running between the poles before going to the combiner?

As most wrenches know, lightning strikes can induce very high voltage on any 
nearby wire runs and that voltage is looking for a path to ground. Equipment is 
damaged when it contributes to that path. If the voltage was induced on the PV 
module frames or wire, an effective ground system will disperse it to ground. 
Key word here is effective. I have seen grounding systems where the installer 
made nice, neat and tight 90° bends in the ground wire. This is a huge mistake 
which can greatly diminish the effectiveness of the ground system.

Larry Crutcher
Starlight Solar Power Systems



On Sep 7, 2012, at 8:40 AM, Jeff Irish wrote:


A customer of ours has recently suffered lightning damage to 31 out of 160 top 
of pole mounted modules.  This is the first time in 10 years that I've seen 
modules damaged by lightning.  Lots of inverter GF fuses and a few inverters, 
but never modules.  We're trying to determine if it was caused by the lightning 
flash irradiating the modules or ground currents.

The array consists of 16 DP&W top of pole mounts with 10 modules each, arranged 
in a square of 4 poles E-W and 4 rows N-S.  The poles are 13 feet center to 
center E-W and the N-S row spacing is about 50 feet.  The poles are 6 inch 
galvanized Technoposts, augured 5 - 7 feet into the firm ground, connected with 
a network of about 160 feet of bare #6 copper and at least 8 copper plated 
ground rods.  Altogether we have about 130 square feet of bare metal surface 
area connected and buried in the ground at and around the array.

The customer saw lightning strike just after dawn a few weeks ago a couple 
hundred feet to the southwest where it also destroyed two utility pole mount 
distribution transformers and ran along the utility wires 100 feet south of the 
array.  The inverters are 200 feet NW and suffered no damage.  The array and 
modules look totally fine, except some of the J-boxes are deformed from heat.  
Opening the J-boxes shows varying levels of damage to one or more diodes, from 
discoloration to being broken and cracked open.

The odd thing is the pattern of damage (we've tested all the modules 
individually for Voc and Isc).  Only modules in the south row of 4 poles are 
damaged, and the damage is concentrated on the modules closest to the ground; 
modules higher up in the air appear OK.  Also, damage is less frequent as you 
move east, away from the direction of the strike.

If it was caused by ground currents, why would the current want to go up the 
poles, why only the southern row of poles, and why damage more modules closer 
to the ground and not those at the top?  Is it possible a flash near the ground 
irradiated the modules causing a current spike and the southern row shielded 
the other rows from most of the flash?  Anyone have experience with this?


Jeff Irish, PE
President
Hudson Solar
13 Hook Road
Rhinebeck, NY 12572
T.845.876.3767x110
F.845.876.3912
[email protected]<mailto:[email protected]>
Solar Electric Systems
NYSERDA Eligible PV Installer
NABCEP Certified Solar PV Installer
NABCEP Certified PV Technical Sales
MailScanner has detected a possible fraud attempt from "applewebdata:" claiming 
to be 
HudsonSolar.com<applewebdata://B5F2562A-2B67-4161-84E4-42F12DC28720/www.hudsonsolar.com>
2011 NYSERDA Excellence in Quality Award | 2011 NYSEIA Award Winner | 2009 Best 
of the Hudson Valley | 2008 SunPower Dealer of the Year | EDC Business 
Excellence Award for Innovation

_______________________________________________
List sponsored by Home Power magazine

List Address: 
[email protected]<mailto:[email protected]>

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org/>


--
This message has been scanned for viruses and
dangerous content by Hudson Valley Computer 
Services<http://www.hvcomputerservices.com/>, and is
believed to be clean.
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to