August:

It's all about safety: If one has a 230V circuit and you are incorrectly using non-handle-tied breakers, when an overcurrent event occurs on only one phase, only one breaker trips. The circuit stops working but the appliance is still energized with the other phase of AC. A repair person may inadvertently assume the circuit is off based on the non-operational status of the appliance and, during repair, come in contact with conductors or equipment energized by the breaker that is still on.

In a correct installation (handle-tied) an overcurrent on one phase de-energizes both phases.

A similar scenario applies in situations with a "multi-wire branch circuit," aka a shared neutral. It is less likely that a dangerous situation will occur because one circuit will still work. Opening the neutral can result in over-voltaging one circuit (been there, bought that replacement cash register). I am not a house electrician, but I think dishwasher / garbage disposal multi-wire circuits require handle ties. Anyone else want to clarify this point?

This is a subtle but important point. This is an example of knowledge that a non-licensed or under-experienced electrician may not posses, hence the desirability of requiring meaningful licensure.

Sincerely,

William Miller



At 03:06 PM 9/25/2012, you wrote:
Hi Wrenches,

Do any of you know the reason why we might use an independent trip versus a common trip two pole breaker for a solar inverter? My understanding is that the independent trip will only trip the individual line effected by the overcurrent condition compared to the common trip which will trip both poles. Both are tied together by a handle tie and both lines must be flipped on at the same time. Cutler hammer is a good example of a company who makes both types.

It seems like supply houses sell both types willy nilly.

Best,

August
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


Internal Virus Database is out of date.
Checked by AVG - www.avg.com
Version: 8.5.455 / Virus Database: 271.1.1/5272 - Release Date: 09/16/12 18:34:00

Miller Solar
Voice :805-438-5600
email: [email protected]
http://millersolar.com
License No. C-10-773985

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to