Midnite Solar is developing what will in essence be an "E-Panel for the Sunny Island". I believe that it is in partnership with SMA-America, given the need for so many third-party components in Sunny Island systems. Midnite is also developing a transformer under the same auspices. My understanding is that products will be shipping in 4-6 months.
Allan

Allan Sindelar
[email protected]
NABCEP Certified Photovoltaic Installer
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder and Chief Technology Officer
Positive Energy, Inc.
3209 Richards Lane (note new address)
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com



On 10/5/2012 9:13 AM, August Goers wrote:
I'm looking forward to checking out the SMA Smartformer. We're sending one
of our guys to SMA training later this month to learn more about it is
depth. Up to date, we used the Outback PSX-240 like the one found here to
120/240 step up:

http://www.altestore.com/store/Enclosures-Electrical-Safety/Miscellaneous-
Electrical-Parts/Transformers/Outback-PSX-240-Autotransformer-with-Fan/p40
89/

My experience with a handful of Sunny Island backup systems has been
really good. The Sunny Island is a very solid piece of equipment and is
easy to program if the plan is properly thought through and everything is
wired properly.

Good luck with your project! -August

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dave Click
Sent: Friday, October 05, 2012 6:01 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] SunnyIsland - was AC coupling and Outback
inverters

Check out the new SMA Smartformer, though I'm not sure whether it's
actually shipping yet. I'm thinking about this for my house eventually
(SB5000US).

http://www.sma-america.com/en_US/products/off-grid-and-back-up-solutions/s
martformer-for-sunny-island.html

Alternatively, the new SMA TL inverters (at least the 3, 4, and 5kW units
according to the press release) have an "Emergency Power Supply"
function that can provide backup power (12A?) during the day when the grid
is down. This may meet your customer's requirements. No batteries
required, though since the TLs require ungrounded arrays, you may need to
rewire the existing array to be compliant with 690.35 (PV Wire or
raceway).


On 2012/10/5 8:41, Kirk Herander wrote:
One Question: Output of the SunnyBoy is 240vac. So this is fed to the
critical load panel, of which the SunnyIsland 120 vac output is fed to.
So we need a 120/240 step up transformer between the SunnyIsland and
the critical load panel to fully take advantage of the Sunnyboy array
for battery charging, correct?.

Kirk Herander

VT Solar, LLC

dba Vermont Solar Engineering

NABCEP^TM Certified installer Charter Member

NYSERDA-eligible Installer

VT RE Incentive Program Partner

802.863.1202

*From:*[email protected]
[mailto:[email protected]] *On Behalf Of
*David Katz
*Sent:* Friday, October 05, 2012 2:11 AM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] AC coupling and Outback inverters

Hi Kirk,

All of the Outback inverters will work AC coupled (GT and FX) as will
any bi-directional H-bridge type inverter.  I have used old Trace
SW's, SunnyIsland, Apollo TSW, Magnum AE and now I am using an Outback
Radian to do exactly what you are talking about.  I have 6 kW of grid
tie inverter and an additional 4kw of modules running through a
Xantrex 600 volt charge controller to the batteries that the Radian
runs on. It all works flawless as long as you have a provision for
protecting the batteries when the gid is down and the grid-tie PV
system is making more power than the loads are using.

If the customer has SMA inverters, I would recommend using a
SunnyIsland because the battery control when the grid goes down is so
elegant.
Everything else is a bit of a kludge.

David Katz

CTO & Founder

AEE Solar Inc

P: 707 825-1200

F: 707 825-1202

[email protected] <mailto:[email protected]>

www.aeesolar.com <http://www.aeesolar.com>

*From:*[email protected]
<mailto:[email protected]>
[mailto:[email protected]]
<mailto:[mailto:[email protected]]> *On Behalf
Of *Kirk Herander
*Sent:* Thursday, October 04, 2012 2:11 PM
*To:* RE-wrenches
*Subject:* [RE-wrenches] AC coupling and Outback inverters

I have AC-coupled an Outback quad-stack with multiple SunnyBoy 6000US
inverters and it's been running fine for 4 years. I used the off-grid
version of Outbacks.

Now I have an application where a customer wants to add battery backup
to an existing SunnyBoy 5000US system. And expand his array by a
couple KW. So I'm thinking of using a GT Outback w/ batteries to
handle the critical loads and feed the extra 2kw of PV (charging the
batteries through an MX60) to the grid. And I'd like to AC-couple the
SunnyBoy so the original 5 kw array can also charge the batteries, BUT
I remember, at least I think so, that the GT inverter cannot be
AC-coupled, only the off-grid version. Is this correct? Thanks.

Kirk Herander

VT Solar, LLC

dba Vermont Solar Engineering

NABCEP^TM Certified installer Charter Member

NYSERDA-eligible Installer

VT RE Incentive Program Partner

802.863.1202



_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to