If it is that type of relay you are searching for, Cooper Power Systems,
Basler Electric and Schneider Electric also make similar products.

 

-Glenn Burt

 

From: [email protected]
[mailto:[email protected]] On Behalf Of Steven
Lawrence
Sent: Wednesday, November 21, 2012 3:11 PM
To: [email protected]
Subject: Re: [RE-wrenches] 15 kV redundant relay

 

Hi Conrad,

 

Without any specs on what the redundant relay is trying to accomplish, I'm
guessing you'll need the SEL 547.  It's a microprocessor relay that takes
voltage and current and will trip a circuit breaker provided you have a set
of PTs and CTs.  

Steven Lawrence

 


Date: Tue, 20 Nov 2012 15:54:24 -0500
From: "conrad geyser" <[email protected]>
To: "'RE-wrenches'" <[email protected]>
Subject: [RE-wrenches] 15 kV redundant relay
Message-ID: <[email protected] <http://cape.com/> >
Content-Type: text/plain;       charset="us-ascii"

Fellow wrenches,

Anybody know a source for a 15 kV"redundant relay" ?  I have a 1 MW farm
ready to go online and the engineering didn't spec. this utility
requirement.   Everybody's many weeks out on producing.

Happy Thanksgiving all,

Conrad
Cotuit Solar

 