jay,

The diversion control has nothing to do with battery current, it is to control voltage. Without it, over-voltage will occur anytime more charge current is available than the battery is accepting. A healthy small battery bank current can be as low as 0.6 amperes for flooded and AGM or GEL technology as low as 0.1 amperes.

Larry Crutcher
Starlight Solar Power Systems
-------- Original Message --------
Subject: Re: [RE-wrenches] Hydro Diversion Controls
From: jay peltz <[email protected]>
Date: Thu, November 22, 2012 12:22 pm
To: RE-wrenches <[email protected]>

Hi William

If the hydro is only 2 amps, I would argue that you don't diversion at all.

The float current expect for a really small battery bank is higher than that.

So unless you want/need it for some other reason, I would not install one.

jay

peltz power
On Nov 22, 2012, at 11:18 AM, William Miller wrote:

> David:
>
> Interesting idea. The added benefit is if the relay gets stuck, it won't destroy the battery bank.
>
> The diversion load must equal or exceed the output of the hydro, correct? The load we have will draw 38 amps at 24 vdc, the hydro will put out 2 amps. Sounds like I have enough headroom
>
> Thanks again to all of you.
>
> William
>
> At 08:32 PM 11/21/2012, David Katz wrote:
>
>> William,
>> I always connect the hydro side of the diode to the diversion load with the contactor, so I don't pull the battery down while regulating. The diversion load must draw enough current to pull the hydro voltage below the absorb voltage. Use ohms law to calculate the resistance.
>> David Katz
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: [email protected]
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to