Peter,

I use a variable 20 amp, 1-30 volt power supply with CC or CV for such 
situations. You can learn a lot by charging individual cells. Plus you can 
raise the voltage up much higher (2.8VPC) without harm as long as you monitor 
temperature. Above 125°, stop charging or reduce voltage. 

If you can't do this, you can continue charging and the low cells will simply 
absorb more current until they reach equilibrium.

With 17 amps current, you are a long way from 100% SoC.


Larry Crutcher
Starlight Solar Power Systems






On Nov 28, 2012, at 1:08 PM, Parrish, Peter wrote:

I didn't want to originally load you guys down with minutiae, but we have been 
having problems keeping the battery bank fully charged. We would put it on the 
charger and after a while it settled down to about 17A, which is about 3.1-3.3% 
of the rated capacity. The total series voltage was 57.9 V. 

We have had a couple of service calls from "Tower of Power". First guy came out 
Monday and determined that two of the batteries had been installed backwards! 
The second guy came out yesterday and replaced the reversed cells. He said that 
the replacement cells were fully charged but they weren't (rested they were at 
2.079 V/cell). They recommended that we put it back on the charger for four 
hours -- I am concerned about this approach, does it work to charge a 24 cell 
bank, with two weak cells in the series? Well, we did for about 30 minutes and 
got the following readings, while charging:

V=57.9 V, 17 amps. Original cells varied around 2.38 V to 2.41 V under charge, 
with the two replacement cells at 2.13 V to 2.14 V. I stopped the charge last 
night, to get more information on how to proceed. 

This morning, the readings were: original cells at 2.128 V to 2.169 V and 
replacement cells at 2.045 V and 2.063 V.

Under the circumstances, how should we bring these two replacement cells up to 
snuff, so that we can operate the system going forward?

- Peter











-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Larry Crutcher, 
Starlight Solar Power Systems
Sent: Wednesday, November 28, 2012 9:06 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Info On 2 V batteries Please

Peter,

To your first question: fully recharging any lead acid battery as soon as 
possible will give you longer cycle life. Waiting to charge and/or deep 
discharges lead to shorter life. If you have the proper 3-stage charger, leave 
it on the battery until you needed to use the forklift.

100% SoC voltage after appropriate rest varies among batteries. I have worked 
with a few forklift batteries in off grid homes. Flooded rest at 2.117 VPC. For 
AGM about 2.183 VPC. (77°F)

As I have posted in the past, most AGM battery can easily withstand up to 5C 
initial charge rate. Proper voltage and time is the more important factor when 
charging AGM's. 

Larry Crutcher
Starlight Solar Power Systems






On Nov 27, 2012, at 2:31 PM, Parrish, Peter wrote:

We recently purchased a battery powered forklift, with 24 ea. 2V batteries. 
Approximate dimensions: W=5", L=6-3/16", H=~21" (hard to tell). Enersys is 
stamped on the top.

The battery supplier claims the batteries are "24-85-13" but this refers to a 
24V battery as far as I can tell. He also claims that the batteries are rated 
at 510-550 A-hr. I am assuming that the lower number is for 6 hours discharge.

I would like to know more about the batteries. Also, how to discharge / charge 
them. Should they be run down to 20% SOC and then fully charged? What if we 
don't use the forklift for a week at a time?

Based on my experience of using AGM batteries, it would seem that the Bulk 
charging rate should be some percentage (e.g. 20%) of the 6-hour ampacity, then 
there is a constant voltage absorption charge (e.g. Vabs=2.385 V), and a switch 
to Float when the charging current drops to some low percentage (e.g. 0.5% of 
capacity), and the Float voltage being 2.125 V. Again everything at 25 deg C. 
It seems like the forklift guys like to refer everything to a 6 hour capacity, 
which may be related to the maximum typical daily usage.

What is the relationship between Voc and SOC after resting the battery for 6 
hours at 25 deg C?

Thanks in advance for your help, guys.

- Peter Parrish

Alternative Energy Department
College of the Canyons
[email protected]
O: (661) 362-3888 C: (323) 839-6108
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]