Hi Lance,

I've checked all the electrical panels and there is no three phase load in the building. It houses a federal facility and their design standard was for three phase. All loads are 120/240. All loads on the EP are 120. Thanks for your help.

Chris
On 11/29/2012 8:32 PM, Darryl Thayer wrote:
This is solvable, first is your needs are for back up at 120-208 3 phase, or can you get by with 120 back up? Or a William suggests 120-240 derived from 120 volt system? The question is do you need 3 phase? Outback using 3 inverters can produce 3 phase. HOWEVER I have never seen two SW generate 3 phase.

------------------------------------------------------------------------
*From:* lance barker <[email protected]>
*To:* RE-wrenches <[email protected]>
*Sent:* Thursday, November 29, 2012 8:29 AM
*Subject:* Re: [RE-wrenches] Connecting Two Grid-Battery Backup Inverters to 120/208

I'm up
On Nov 28, 2012, at 8:30 PM, William Korthof wrote:

> You could use a 120:120volt, with both the first and second inverters using the same phase, but the xfmr secondary used to supply 120 volts out of phase from the primary for the slave. Voila, auto-transformer 120:240 split phase power. Downsides are the heavy loading all on one phase and neutral, and xfmr losses...
>
> Alternate option is to get an isolation transformer with 208 primary and 120/240 secondary. Bond the midpoint.
> Better phase balance, but xfmr losses.
>
> /wk
>
> William Korthof
> 714.875.3576
> Sustainable Solutions
> #956904
>
> -------------------------
> From: Christopher Warfel
>
> We were asked to replace two failed Trace SW4048 inverters with two
> Outback GT3048 inverters. Upon start up the slave inverter would not
> connect.  We did not realize that the building service is 208, 3 phase.
> The bypass is 120/240 which the SW4048s could connect to without a
> problem. Outback says their inverters will not connect to this system
> because of the phase angle of 120 and their software.
>
> The phases are always going to be at this rotation, so I don't see a
> transformer helping solve the problem, but this is something I am really
> unfamiliar with.
>
> So the input at the inverter panel is two 120 volt phase at 120 degrees.
> The output to the EP is 120/240.
>
> I am asking if anyone has an idea of how to fix this problem?
> ------------snip---------------
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: [email protected] <mailto:[email protected]>
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
>
> Check out participant bios:
> www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected] <mailto:[email protected]>

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org





_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


--

Christopher Warfel, P.E.
ENTECH Engineering, Inc.
Energy Utilization Experts
(401)466-8978

The information contained within this communication shall
be considered confidential and shall not be retransmitted
without knowledge of the sender. Please contact us if
this email reached you in error. Thank you.

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to