SMA Sunny Island also does this but also discharges battery in parallel with 
the generator to create a "virtual generator" that is larger than the actual 
generator.
Just set the max generator current and it does the rest.

Best Regards,

John Berdner
General Manager, North America

[cid:[email protected]]

SolarEdge Technologies, Inc.
3347 Gateway Boulevard, Fremont CA 94538 USA  (*Please note of our new address.)
T: 510.498.3200, X 747
M: 530.277.4894

From: [email protected] 
[mailto:[email protected]] On Behalf Of Allan Sindelar
Sent: Thursday, January 31, 2013 2:14 PM
To: William Miller
Cc: RE-wrenches
Subject: Re: [RE-wrenches] Husqvarna 5500 and VFX3524 Compatibility question

William,
Yes, that's my understanding. Outback acknowledged this to me years ago.
Allan
Allan Sindelar
[email protected]<mailto:[email protected]>
NABCEP Certified Photovoltaic Installer
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder and Chief Technology Officer
Positive Energy, Inc.
3209 Richards Lane (note new address)
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com<http://www.positiveenergysolar.com/>


On 1/29/2013 9:28 PM, William Miller wrote:
Allan:

Could it be that the SW systems are protecting the generator with Generator 
Support, and the Outback inverters are not?

William Miller



At 07:18 PM 1/29/2013, you wrote:

This is going back several years...

The Outback VFX series lacks the tight input current regulation of the SW 
series, so the max AC amps in is really just a suggestion. In many cases (and 
especially with these small generators) we want to set the max amps in as high 
as possible to minimize charging time and maximize C/rate. Yet a surge load can 
momentarily exceed the max amps setting.

I have observed that the Honda inverter/generators have a quite sensitive AC 
output breaker, that will sometimes trip if a surge load (such as a 
refrigerator) comes on during a charge cycle set close to the generator's 
capacity. This incident was specific to a Honda 3000i. In contrast, Yamaha's 
EF3000iSE will lug when overloaded - not good for the generator, but also not 
likely to trip the output breaker.

This is a different issue than was being discussed, but fits your question.
Allan

CONFIDENTIALITY NOTICE: This e-mail and its attachments are intended only for 
the use of the individual or entity who is the intended recipient and may 
contain information that is privileged, confidential and exempt from disclosure 
or any type of use under applicable law. If the reader of this e-mail is not 
the intended recipient, or the employee, agent, or representative responsible 
for delivering the e-mail to the intended recipient, you are hereby notified 
that any dissemination, distribution, copying, or other use of this e-mail is 
strictly prohibited. If you have received this e-mail in error, please reply 
immediately to the sender.
P  Please think of the environment before printing this email

<<inline: image001.jpg>>

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to