Allen,
The benefit I see would be to allow for a code compliant load side
connection on a 200A panel with a 200A MB, where the AHJ is on the
2008 NEC or older and will not listen to your good logic. I don't
think this would always be the best option, but if backup loads and
inverter output were less than 32A then a 40A OCPD in the main panel
should be fine? Since it sounds like the 60A breaker in the main
panel is not a safety issue, but a design consideration, I suppose I
would just prefer flexibility when possible.
That said, this AHJ is on the 2008, and the loads will be less than
30A, but based on this conversation I plan to go with a 60A and try
to convince the AHJ that it will be code compliant in their future!
Thanks,
Garrison
*From:*[email protected]
[mailto:[email protected]] *On Behalf Of
*Allan Sindelar
*Sent:* Thursday, February 28, 2013 8:14 AM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Conductor Sizing for Supply Side Connection
Garrison,
I don't know why it's not listed as 60A max, but my own internal
logic would ask why it should be. The only benefit I could see for
using smaller than a 60A breaker would be to allow use of #8
conductors (allowed with a 40A or 50A breaker) instead of the #6
necessary with a 60A breaker. And of course, you could use a 40A
breaker with #6 conductors, so theoretically it would be fine. I just
fail to see any benefit to doing so.
Allan
*Allan Sindelar*
[email protected] <mailto:[email protected]>
NABCEP Certified Photovoltaic Installer
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder and Chief Technology Officer
*Positive Energy, Inc.*
3209 Richards Lane (note new address)
Santa Fe, New Mexico 87507
*505 424-1112*
www.positiveenergysolar.com <http://www.positiveenergysolar.com/>
On 2/28/2013 6:27 AM, Garrison Riegel wrote:
Thanks Allen for clarifying why a 60A is required. I was
wondering. The spec does list a surge current of 9000W so I
thought that may be the rationale, but even that would only
require a 50A, and since this surge occurs during 'stand-alone
mode' it didn't seem to apply to the OCPD at the main panel.
Your explanation makes more sense, but I wonder why then they
don't list the AC input breaker size as 60A /max/. If you have
few backup loads, and are not on the 2011 NEC, a 40A could
theoretically be fine?
Thanks all for your thoughts, much appreciated.
Garrison
*From:*[email protected]
<mailto:[email protected]>
[mailto:[email protected]] *On Behalf Of
*Allan Sindelar
*Sent:* Wednesday, February 27, 2013 6:08 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Conductor Sizing for Supply Side
Connection
August,
The 60A breaker is intended to allow grid power to pass through
to the loads in excess of the inverter's stand-alone output. The
point of 705.12 (moved in the 2011 NEC from 690.64 (B)(2)) is to
differentiate between load pass-through current and sell current.
The amount of current fed into the grid is (4500/230 =) 19.56A,
while the amount that can be taken from the grid and passed
through to the load is much greater. If you were limited to a 40A
breaker in order to maintain 120% of a 200A main bus, you'd be
prone to nuisance trips under large cumulative loads.
Allan
*Allan Sindelar*
[email protected] <mailto:[email protected]>
NABCEP Certified Photovoltaic Installer
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder and Chief Technology Officer
*Positive Energy, Inc.*
3209 Richards Lane (note new address)
Santa Fe, New Mexico 87507
*505 424-1112*
www.positiveenergysolar.com <http://www.positiveenergysolar.com/>
_______________________________________________
List sponsored by Home Power magazine
List Address:[email protected]
<mailto:[email protected]>
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
<http://www.re-wrenches.org/etiquette.htm>
Check out participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org>
_______________________________________________
List sponsored by Home Power magazine
List Address:[email protected]
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios: