Lou:

Allan presents the better advice below. Ignore my previous post until you are sure the battery is bad.

William Miller



At 02:57 PM 3/15/2013, you wrote:
Lou,
There is nothing in your message that definitively tells me that you have either a bad cell or a bad battery. "Minor corrosion on one terminal" is normal behavior, especially if the installer didn't coat the terminals at installation. "One cell was not using as much water as all the rest" is a matter of perception. You write yourself that "everything looked fine." It seems to me that you're jumping to conclusions based on the comment of another Wrench without doing sufficient testing first. Get the client to put a measured load on the system without charge. This isn't hard to do with an amp-hour meter in the system - you want a steady load of about 55 A (a C/20 load). If you have a bad cell, it'll show up soon enough.

For now, I'm on Interstate's side.

Hope this helps,
Allan