Hi Dan,
You can do it!
You are looking for a circuit called a crowbar. It is a SCR that turns
on when a certain voltage is exceeded. Typically implemented with an SCR
and a zener diode. The SCR, when turned on, shorts out the battery. And
BAM you blow the big fuse in the battery bank or before the load you are
trying to protect. So the SCR needs to be able to handle the fuse
blowing current for just long enough to blow the fuse.
http://en.wikipedia.org/wiki/Crowbar_%28circuit%29
You could make a variant of this that trips a shunt trip circuit
breaker. Midnite sells some shunt trip breakers that could be suitable.
More expensive to do it this way, however.
-James Jarvis
APRS World, LLC
On 3/15/2013 10:05 PM, Dan Fink wrote:
This has been happening all too frequently here. We live in a big area
of off grid homes, dozens of systems.
Lost a customers Trace 2624 this morning; One L-16 in older 24v bank
opened internally. PV array/MPPT control zorched inverter as soon as
the sun came up. First indication of problems last nite when customer
hit microwave to warm up dinner and inverter went crazy. This morning
the bad battery showed 3.2v (yes, I would expect 2 or 4 also) the rest
the usual 6+v. Turned on PV array, bad battery immediately up to 11v
(yes, 6v L16).
Somebody needs to build a "battery condom" with big stacked diodes on
a big heat sink or some such solution. A voltage brick wall for system
charging inputs. MPPT PV controllers do NOT protect a inverter from
input overvoltage if all or part of the battery bank disappears! And
last year we saw a nice battery box fire and zorched inverters due to
similar -- dual 48v L16 strings, one cell failed and opened, other
string dumped everything into the bad one, smoke and flames. Parallel
fusing would have stopped that......but not stopped the loss of dual
stacked XW inverters from PV overvoltage.
Or am I missing something here?
Dan Fink,
Executive Director;
Otherpower
Buckville Energy Consulting
Buckville Publications LLC
NABCEP / IREC accredited Continuing Education Providers
970.672.4342
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
--
-James Jefferson Jarvis
APRS World, LLC
+1-507-454-2727
www.aprsworld.com
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org