I have found w/ our off grid sites we recommend to our clients to repel the 
mate once every a couple months. Perhaps this has changed but just another 
tweak.
On Mar 27, 2013, at 5:28 PM, Randy Brooks wrote:

> Drake,
> 
> If the generator has a two wire auto start/stop, then a relay connected to 
> the master FX AUX output, that opens and closes the auto start circuit, has 
> worked reliably for us on a number of systems.  No need for a GSCM.
> 
> Just be sure all the FX charger settings, and MATE AGS settings are as 
> desired.  In particular, be sure the DC GENSET is set to "NO", and the VDC 
> GENSTOP is set to a high value that will never be reached during normal 
> generator charging (the default is high enough).  The VDC GENSTOP will turn 
> off the generator even if DC GENSET is set to "NO".  If the value is too low, 
> the normal FX charging cycle will be interrupted prematurely.
> 
> Good luck,
> 
> Randy Brooks
> Brooks Solar, Inc.
> Solar Power for People
> 140 Columbia View
> Chelan, WA  98816
> 509-682-9646
> [email protected]
> www.BrooksSolar.com
> 
> On Mar 27, 2013, at 12:51 PM, Drake <[email protected]> 
> wrote:
> 
>> Hello Wrenches,
>> 
>> We are adding a Generac EcoGen to an existing Outback VFX 3648 system.  It 
>> was the recommendations from those of you on this list who have installed 
>> them that led to this choice. Your testimonials are very much appreciated.
>> 
>> I've read, on this list, that people have had issues with FX family 
>> inverters starting and stopping generators reliably. The plan was to go with 
>> the Atkinson GSCM and a separate voltage controlled relay.  It appears that 
>> if the system is 48 volts, it is necessary to center tap the battery bank 
>> for a 24 volt feed to the GSCM. This I don't want to do.
>> 
>> Is it still agreed that the FX inverters are not reliable for starting and 
>> stopping generators? 
>> 
>> Has anyone used a GSCM on a 48 volt system without problems?
>> 
>> Thank you,
>> 
>> Drake 
>> 
>> 
>> 
>> 
>> 
>> 
>> 
>> Drake Chamberlin
>> Athens Electric LLC
>> OH License 44810
>> CO License 3773
>> NABCEP Certified Solar PV Installer
>> 740-448-7328
>> http://athens-electric.com/ 
>> 
>> _______________________________________________
>> List sponsored by Home Power magazine
>> 
>> List Address: [email protected]
>> 
>> Change email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: 
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out participant bios:
>> www.members.re-wrenches.org
>> 
> 
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: [email protected]
> 
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 

> [email protected]               www.SWNL.net
>                 Solarwinds Northernlights       
>        Serving Mid Coast Maine & Northern California
>                          207-832-7574   Cl. 610-517-8401                      
>         
>                               Blair "TUMP" May
>                ********  MAINE'S CHARTER ********
>                       NABCEP    "Certified PV Installer" 
>    
>               ********  MAINE'S CHARTER ********
>                   Trace Xantrex "Certified" Dealer / Installer"
> 


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to