Nathan:

You can find 1000 V rated PV wire from a number of sources.
A simple google search for "UL4703 PV Wire" will yield several choices.
PV wire is approved for use  in conduit but you will need to calculate the 
conduit fill factors manually since the outside diameter is larger than the 
"standard sized wires"

Conduit is not an issue @ 1000V but switchgear, combiners and fuses are a bit 
harder to find (but not impossible).
Not sure of the specifics of the system so it is hard to make detailed 
recommendations.

Best Regards,

John Berdner
General Manager, North America

SolarEdge Technologies, Inc.
3347 Gateway Boulevard, Fremont CA 94538 USA  (*Please note of our new address.)
T: 510.498.3200, X 747
M: 530.277.4894

From: [email protected] 
[mailto:[email protected]] On Behalf Of Nathan Stumpff
Sent: Friday, March 29, 2013 12:09 PM
To: [email protected]
Subject: [RE-wrenches] 1000 Vdc

Wrenches,

This is an offshoot in a way to the Cable Tray discussion, but until there are 
Brits running my permit office...

I am considering pitching a 1,000 Vdc system to my AHJ, and it seems like the 
solar components (modules, inverters, combiners, array wire) are the easy part 
in a lot of ways.

We use Cerro XHHW-2 for basically all of our wiring outside of an array, and it 
is clearly marked 600 V. Does anyone have a good resource for wire, conduit, 
fittings, junction boxes, etc. that carries a 1000 Vdc rating? Does anyone know 
of a 1,000 Vdc rated PV Wire that can be run in conduit in a building?

Any info appreciated, thanks,
-Nathan

--
Nathan J. Stumpff
NABCEP Certified PV Installer #091209-175
NABCEP Certified Solar Heating Installer #032412-14
Project Manager | Arctic Sun, LLC
[email protected] <mailto:[email protected]>  | (907) 457-1297
www.reina-llc.com<http://www.reina-llc.com> | 
www.arcticsun-llc.com<http://www.arcticsun-llc.com/>
[cid:[email protected]]<http://www.facebook.com/ArcticSunLLC>

CONFIDENTIALITY NOTICE: This e-mail and its attachments are intended only for 
the use of the individual or entity who is the intended recipient and may 
contain information that is privileged, confidential and exempt from disclosure 
or any type of use under applicable law. If the reader of this e-mail is not 
the intended recipient, or the employee, agent, or representative responsible 
for delivering the e-mail to the intended recipient, you are hereby notified 
that any dissemination, distribution, copying, or other use of this e-mail is 
strictly prohibited. If you have received this e-mail in error, please reply 
immediately to the sender.
P  Please think of the environment before printing this email

<<inline: image001.png>>

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to