Larry

I believe that APS ( Bluefrog <http://bluefrogsolar.com/aps-inverters>)
micro inverters can be adjusted down to 180 VAC, so they should  work line
to line in your application. I know that their spec sheet and manual do not
indicate that, but I have installed them in adjusted for a 208 VAC and they
have been sending adjusted units to Hawaii.  You will probably have to
contact them directly to see what can be done.

Bill


On Mon, Apr 15, 2013 at 1:25 PM, Larry Crutcher, Starlight Solar Power
Systems <[email protected]> wrote:

> Wrenches,
>
> A customer in Mexico wants to start with about 10kW PV. They have a 225
> kva transformer supplying 220/127 volt 3-phase to the property. They are
> adding buildings/roof space in several stages over the next 4 years and
> want to grow the installation to 120kW of PV solar power.
>
> Manufacturer data sheets are not real clear. Who makes micro-inverters
> suitable for this? I know Enphase does not.
>
> Thank you,
>
> Larry Crutcher
> Starlight Solar Power Systems
>
>
>
>
>
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: [email protected]
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Bill Hoffer
P.O. Box 1823
White Salmon, WA 98672
[email protected] <[email protected]>
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to