Good info, I thought maybe the warm days the system might drag the voltage to 
low, that's why I asked.  

So, on to MPPT controllers.  Again limited use, so looking for some good info.  
Kinda limited battery experience to be honest.  Just very small cabin/shacks.  
Rewiring an array in this scenario would increase voltage to the controller, 
and the controller then sacrifice (for lack of a better word) voltage and 
increase the current?  Just looking at the ISC numbers of the array now it 
produces 69.2 at STC, would the re-wired array produce similar current but 
match programmed setpoints? 

Jesse
 

Sent from my iPhone

On May 13, 2013, at 9:51 PM, Kirpal Khalsa <[email protected]> wrote:

> Jesse.....why wouldn't you wire at least 2 modules in series....this way you 
> have less breakers to deal with, less cord grips if paralleling in a combiner 
> box, less homerun cables to the combiner and you will also benefit from 
> greater energy harvest in your MPPT conversion particularly during cold 
> weather....
> If you go with 1 module strings and have hot weather your voltage sag in the 
> summer you will be on the low edge of voltage window to properly charge a 24V 
> battery bank.....
> i would check the charge voltage recommendations from the battery 
> manufacturer for proper charging parameters....usually the voltage 
> recommendations call for lower voltages than FLA batteries...may be helpful 
> for being able to charge your sealed batteries from a single module.  It is 
> still borderline...
> I have always believed that the 60 cell modules were a bit on the low side 
> for 24V battery charging.  In the past that is what the 72 cell  modules were 
> for....but those are fewer and farther between these days, except int he 
> larger 300+ watt modules....
> If you had 9 modules i would even go with strings of 3....or if you want to 
> get really efficient you could wire in strings of 4 with the Midnite Solar 
> Classic 200 charge controller.....you would definitely be bumping into 
> amperage limits.....but that is ok...
> good luck...
> 
> 
> Sunny Regards,
> Kirpal Khalsa
> NABCEP Certified PV Installation Professional
> Renewable Energy Systems
> www.oregonsolarworks.com
> 541-218-0201 m
> 541-592-3958 o
> 
> 
> On Mon, May 13, 2013 at 7:34 PM, Jesse Dahl <[email protected]> wrote:
>> Hello,
>> 
>> I'm interested in charging voltages for AGM batteries. After my visit to the 
>> site mentioned in the battery box thread, I was thinking about the system.
>> 
>> New install, 8 solarworld 255s charging a 24V battery bank through a outback 
>> FM80 (MPPT) All 8 modules in parallel.
>> VOC - 37.8
>> VMP - 31.4
>> ISC - 8.66
>> IMP - 8.15
>> 
>> I'm interested in the setpoints people use for AGMs because it seems like 
>> this might be cutting it close to the setpoints based on the array voltage. 
>> Since the system is using a MPPT controller would it be better to increase 
>> the array voltage?
>> 
>> Battery bank is 6 12V 245ah east penn bats wired 3 strings of 2.
>> 
>> I haven't used sealed batteries outside my fish house and boat so I'm 
>> looking for some detailed info if I can get it.
>> 
>> Thanks a lot!
>> 
>> Jesse
>> 
>> 
>> Sent from my iPhone
>> _______________________________________________
>> List sponsored by Home Power magazine
>> 
>> List Address: [email protected]
>> 
>> Change email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: 
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out participant bios:
>> www.members.re-wrenches.org
> 
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: [email protected]
> 
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to