Ken,

We installed our first Enphase units in Dec 2009, and our *last* Enphase
units in 2011.  The breaking point for me was when the first 215 failed
about 6 weeks into production, oozing black slime out of the case.  Enphase
did two complete system for us last year(one M190 and one D380 site), when
they hit failure rates of 23.7% and 25% respectively.  It seems the wind
has shifted at Enphase lately though.  We had another site hit 28.6%
failure rate this spring and asked Enphase to upgrade the site to 215s.  No
dice.  Here is the response from Enphase:

" As we discussed we would like to start a 90-day monitoring cycle for the
XXXXXXX site. During this process a hold on any current replacements and
monitor the site to see the site stabilizes. A check will be completed
every 30-day to assess the site for any production issues. After the 90-day
monitoring period replacement devices will be sent out. The customer will
also be reimbursed for any loss of production seen during that time.

At the end of the monitoring cycle the site will be assessed if a more
aggressive approach is necessary."

Needless to say neither the customer or myself were happy with the
response.  This weekend we had another site hit 19% failure rate ( four
failures since the beginning of the year)

How long will we be in this mess?  Looks like awhile longer.

I've attached a little table with failure rates for our Enphase systems.

With Regards
Carl Adams
SunRock Solar



>

Attachment: Enphase Failures Summary.pdf
Description: Adobe PDF document

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to