Esteemed Wrenches,

We are having a hard time finding a source of PV Wire with a 1000V rating that 
will fit into a two-hole 1/2" strain relief. It seems that all of the wire 
brands that are "double-insulated" just have too large of a diameter to get two 
of them though a 1/2" strain relief, needed since most common combiners have 
1/2" knockouts for wire entry. However, we have found a source of 
single-insulated wire that is UL Listed and bears the "PV Wire" marking.

I've always been under the assumption that "double-insulated wire" was 
necessary when using transformerless grid-tie inverters, as it is with power 
tools that only have two-prong plugs on them. However I can't find that 
specific language in the Code. It just says "must be marked as PV Wire". I also 
found this quote about PV Wire from John Wiles (underlining mine):

"The thickness is specified and there may be one or two layers of insulation. 
The insulation must pass an accelerated UV test of 720 hours and will be
marked "Sunlight Resistant." PV cable/PV wire also has smoke and 
flame-retardants and may be used inside conduit inside buildings. In the U.S., 
it should
not be called a 'double-insulated cable' as that is a purely European term."

This appears to mean that double-insulation is not required for transformerless 
(non-isolated) inverters; just that it needs to be marked as "PV Wire". Can 
anyone here confirm, hopefully with documentation, that actually having 
"double-insulation" is not required when using non-isolated inverters?

Thanks


Brian Teitelbaum
AEE Solar
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to